Running a 20 amp circuit to a shed

19 posts in this topic

How deep does the trench need to be? I believe that there is one depth for wire in conduit and one for just buriable wire?

I need to run 80 feet, will 12 gauge wire be enough? Just one outlet and a motion light.

Share this post


Link to post
Share on other sites

Need more information.

Are you going to be on a GFCI breaker or GFCI protected circuit or an a regular breaker?

If you are going to put it on a GFCI breaker and use UF wire the trench has to be NO LESS than 12 inches deep.

Share this post


Link to post
Share on other sites

When i ran a line out to my building it was a 20 amp with a seperate box with GFCI and they enclosed the wire in a tube and we made it 36". Of course we were running gas line also and that was in a seperate trench at 36"...so maybe thats why we put both at 36".

Share this post


Link to post
Share on other sites

As said, check your codes.

Where I live it has to be down 18in.... I would run it in pipe that way you can always

upgrade. Also a little more shovel prof. Make a map with locations on it.

If you are going to put spotlights in you fixture and a 80 foot run, you

better stay with 10ga. wire.

Share this post


Link to post
Share on other sites

Need more information.

Are you going to be on a GFCI breaker or GFCI protected circuit or an a regular breaker?

If you are going to put it on a GFCI breaker and use UF wire the trench has to be NO LESS than 12 inches deep.

Share this post


Link to post
Share on other sites

You better get right on it if you are planning to get it done yet this year. Depending on your soil type most times homeowners and do it yourselfers will use UF cable because of cost and ease of installation. Depending on where you picking the up from you may not need to add a GFCI receptacle or breaker. If the circuit is not GFCI protected already you will need to add either a GFCI breaker or GFCI receptacle. You will find breaker cost of $30.00 and receptacle cost $5.00.

If I was doing what you say it would be 12/2 UF w/ground direct buried and a GFCI receptacle.

UF Cable minimum of 24 inches. Unless covered by 2”-4” of concrete.

PVC Conduit minimum of 18 inches.

Share this post


Link to post
Share on other sites

fishingishot is definatly on the money. Any of those uses would be acceptable. But i would still looking into it further. As some city codes may differ.

Share this post


Link to post
Share on other sites

The NEC (National Electrical Code) article 300.5 states that;

Residential branch circuits rated 120 volts or less with GFCI protection and maximun overcurrent protection of 20 amps you need to be 12 inches deep.

You will need 18" if you are running under an airport or adjacent areas but not in your backyard. You will also need 18 inches if running UF wire in places that are not residential, but, and I repeat, article 300.5 states that for residential use, 120 volts or less and GFCI protected, 12 inches. You can get by with 6 inches deep if you want to put it under 2" or concrete if you want to.

In the residential column, the only places you need to be more than 12" is under streets, road and such or airports, neither of which fit into this particular project.

Thats the issue I have with the code book and not knowing how to read it. I've said it before and I'll say it again. Not all rules apply to all situations. What someones cousin did in their shed dosen't mean the same rules will apply to the bathroom in a church. Without knowing exactly what it says and how to read it, no advice is better than bad advice.

10 ga wire would not be the way to go for this application, heres why. You are allowed 3% voltage drop, by code. 12 ga UF wire will excede 3% at a 12 amp load. With 10 ga wire you will be at 3% with a full 20 amps.

Share this post


Link to post
Share on other sites

If I was doing what you say it would be 12/2 UF w/ground direct buried and a GFCI receptacle.

UF Cable minimum of 24 inches. Unless covered by 2”-4” of concrete.

PVC Conduit minimum of 18 inches.

Where are you getting your information? 18" for PVC is under driveways, not backyards. If you are looking at 300.5 look at column 4. Column 4 is for residential, column 1 is direct bury cables (UF) and column 3 is nonmetalic conduit (PVC). This application falls into column 4

The advantage of going to the breaker is that the circuit will be dedicated and for lack of a better term, all of the electricity in the circuit will be available for you. If you tie into the load side of a GFCI receptacle it will still be 100% legal but you will have to share the power with other items.

Share this post


Link to post
Share on other sites

Is it worth it or not? That is the question. Go to your rental center and rent a trencher. Put it as deep as the trencher goes (usually about 3 ft. or so). This will cost you about $100. The wire will be another $100-$200, and then get an electrician quote. For a small job they will probably charge you a little more than usual. This will cost you at least $400.

I think this is the initial answer you were looking for. If you want to tackle it yourself, there is some good advise here, especially from the electricians here.

Share this post


Link to post
Share on other sites

BTW, frost does break wires, so make sure it is deep and loose.

Share this post


Link to post
Share on other sites

Roofer dude,

I'm just stating what it HAS TO BE, as in the minimum. The NEC tells you the minimum required. Heck, if you want to you could put it in rigid pipe, encase it in 4" of concrete and run 500MCM wire out there if you want to. That would be legal too.

Share this post


Link to post
Share on other sites

Didn't mean anything by it mnfishinguy. I know that you know your stuff and I'm sure it is well appreciated by many. smile

Share this post


Link to post
Share on other sites

I wouldn't say "many" wink It's an interesting book, I recomend it to anyone needs to go crazy. It would be nice if more of the codes "where across the board" but then agian, that's what they pay me for, is to know when to apply what rule to what situation.

Share this post


Link to post
Share on other sites

I wouldn't say "many" wink It's an interesting book, I recommend it to anyone needs to go crazy. It would be nice if more of the codes "where across the board" but then again, that's what they pay me for, is to know when to apply what rule to what situation.

I would like to have a dollar every time they say "shall and shall not" grin

Share this post


Link to post
Share on other sites

There can be other questions as well. Will you be running under an area where vehicles drive? If so, code is different.

Bob

Share this post


Link to post
Share on other sites

Roofer dude,

I'm just stating what it HAS TO BE, as in the minimum. The NEC tells you the minimum required. Heck, if you want to you could put it in rigid pipe, encase it in 4" of concrete and run 500MCM wire out there if you want to. That would be legal too.

I can't help but poke a little fun here.

It would be legal if the circuit components could handle the 500MCM. I'm thinking it would not be legal to use it to supply a 30A panel.

Bob

Share this post


Link to post
Share on other sites
Guest
This topic is now closed to further replies.
Sign in to follow this  
Followers 0



  • Posts

    •   Mike, I have used the brown sugar cure from Curly's to cure a hind leg and it made the best ham I've ever had. They have very detailed instructions on their site, too. I cured it 8 days and it took 18 hours to smoke. Worth every second!   https://web.archive.org/web/20150915234555/https://www18.corecommerce.com/~csk/uploads/file/Smoked Ham or Picnic Recipe(1).pdf
    • i dont use newspaper but use alot of grass clippings. and by late fall there pretty much all rotted away..........good for the garden too!!!!   if you know someone with a lawn care business get ahold of them, i went to a recycling place that takes grass clippings, and in the town i live in anyway, once they get there they dont allow people to come and take them. apparently something to do with potential lawn chemicals. i now get them from the city, they come from the baseball park in town!!!!!
    • Good luck walleye, sorry about the miss, but we all know what a tough road archery hunting can be.   My good friend Dave and I headed to Wisconsin Wednesday afternoon.  We have two tags each. We hunted hard for most of 5 days while enduring some of the worst weather we ever we had to deal with. 40 degrees ain't bad, and a little rain ain't bad, but a hard rain at 40 degrees just plain sucks. Add in some wind and it was pretty miserable.   Wednesday we got to our hunting spot mid afternoon and set up. We weren't intent on spending the evening with plans to scout a bit and get the permission we needed for another farm.  We actually heard a couple gobbles and they seemed to be coming closer, then the rain started.  Do we wait till it quits, or do we leave before it gets worse? Dave said lets get out while we can. Sure enough, as soon as we got out of the blind there was a big tom looking at us.  Game over.  Oh well.   Next morning we were back at this same spot. Nothing going except a lone hen way out, not even a gobble...till 10:00. This bird would gobble and come closer, then gobble as he went farther away. Over and over again.  Finally he showed himself at the end of the field 80 yds out.  He'd gobble then head back into the woods to gobble some more.  In and out like that for what seemed forever. Finally he came back out again and ever so slowly headed our way. Closer and closer, then - "there's another one!"  Another big tom came to see what all the noise was about.  The first one was inching closer and closer, right to the edge of my shooting range. He stopped and lifted his head and turned around. I couldn't wait to see if he'd come closer, a few steps would put him out of range.  My trusty old 870 barked and he was down.  Sweet!  I looked at the clock, it was 11:30. We'd been working this bird for an hour and a half! I later paced it off at 45 yds.  Haven't shot very many beyond that.   The other bird didn't even flinch, he was coming to see why his bud wasn't getting up. Closer and closer till Dave couldn't wait anymore.  He shot. The bird started running, then took flight.  He shot again and that bird was in the woods, never to be seen again.   Two missed opportunities on our first two sits.   Though we hunted hard the next few days and saw some birds, we never had another chance.  Tough, tough hunting.   My bird tipped the scales at just under 24 1/2 lbs. Spurs both right at 1" and pretty sharp, beard just over 10". Probably a 3 year old.
    • Went to the DNR site. Got my tag for area 47 after 4 Years!!  YEA!!   Rockn Randy
    • Lost 40 a few years back. Forget diets, you need an entire lifestyle change. Think of food as either slowly killing you or helping you live longer and healthier. Just because someone is skinny does not mean they are healthy. Personally I stick to a lot of fruits, veggies and wild game, very little carbs, dairy, beef or pork. Not that I don't love ribs, steak & the like but it's not a regular meal. After a while you don't really miss the bad stuff because you feel so much better.   Let me guess, you sell diet supplements in on of those pyramid scheme multi level marketer deals.
    • Old newspapers and grass clippings. The problem with wood mulch is it will still be there in the fall when you want to till the garden.
    •   Best thing I've seen is just old newspapers.      
    • I wanna mulch around my tomatos and peppers this year to keep the dirt from splashing all over them. Was wondering if its bad for them. Was gonna use cedar but was hoping for some advice.
    • Have both a Habanero and a Ghost Pepper in this years garden.   
    • I may have to pick some up I never had time to start my seeds indoors this year
  • Our Sponsors