Running a 20 amp circuit to a shed

19 posts in this topic

How deep does the trench need to be? I believe that there is one depth for wire in conduit and one for just buriable wire?

I need to run 80 feet, will 12 gauge wire be enough? Just one outlet and a motion light.

Share this post


Link to post
Share on other sites

Need more information.

Are you going to be on a GFCI breaker or GFCI protected circuit or an a regular breaker?

If you are going to put it on a GFCI breaker and use UF wire the trench has to be NO LESS than 12 inches deep.

Share this post


Link to post
Share on other sites

When i ran a line out to my building it was a 20 amp with a seperate box with GFCI and they enclosed the wire in a tube and we made it 36". Of course we were running gas line also and that was in a seperate trench at 36"...so maybe thats why we put both at 36".

Share this post


Link to post
Share on other sites

As said, check your codes.

Where I live it has to be down 18in.... I would run it in pipe that way you can always

upgrade. Also a little more shovel prof. Make a map with locations on it.

If you are going to put spotlights in you fixture and a 80 foot run, you

better stay with 10ga. wire.

Share this post


Link to post
Share on other sites

Need more information.

Are you going to be on a GFCI breaker or GFCI protected circuit or an a regular breaker?

If you are going to put it on a GFCI breaker and use UF wire the trench has to be NO LESS than 12 inches deep.

Share this post


Link to post
Share on other sites

You better get right on it if you are planning to get it done yet this year. Depending on your soil type most times homeowners and do it yourselfers will use UF cable because of cost and ease of installation. Depending on where you picking the up from you may not need to add a GFCI receptacle or breaker. If the circuit is not GFCI protected already you will need to add either a GFCI breaker or GFCI receptacle. You will find breaker cost of $30.00 and receptacle cost $5.00.

If I was doing what you say it would be 12/2 UF w/ground direct buried and a GFCI receptacle.

UF Cable minimum of 24 inches. Unless covered by 2”-4” of concrete.

PVC Conduit minimum of 18 inches.

Share this post


Link to post
Share on other sites

fishingishot is definatly on the money. Any of those uses would be acceptable. But i would still looking into it further. As some city codes may differ.

Share this post


Link to post
Share on other sites

The NEC (National Electrical Code) article 300.5 states that;

Residential branch circuits rated 120 volts or less with GFCI protection and maximun overcurrent protection of 20 amps you need to be 12 inches deep.

You will need 18" if you are running under an airport or adjacent areas but not in your backyard. You will also need 18 inches if running UF wire in places that are not residential, but, and I repeat, article 300.5 states that for residential use, 120 volts or less and GFCI protected, 12 inches. You can get by with 6 inches deep if you want to put it under 2" or concrete if you want to.

In the residential column, the only places you need to be more than 12" is under streets, road and such or airports, neither of which fit into this particular project.

Thats the issue I have with the code book and not knowing how to read it. I've said it before and I'll say it again. Not all rules apply to all situations. What someones cousin did in their shed dosen't mean the same rules will apply to the bathroom in a church. Without knowing exactly what it says and how to read it, no advice is better than bad advice.

10 ga wire would not be the way to go for this application, heres why. You are allowed 3% voltage drop, by code. 12 ga UF wire will excede 3% at a 12 amp load. With 10 ga wire you will be at 3% with a full 20 amps.

Share this post


Link to post
Share on other sites

If I was doing what you say it would be 12/2 UF w/ground direct buried and a GFCI receptacle.

UF Cable minimum of 24 inches. Unless covered by 2”-4” of concrete.

PVC Conduit minimum of 18 inches.

Where are you getting your information? 18" for PVC is under driveways, not backyards. If you are looking at 300.5 look at column 4. Column 4 is for residential, column 1 is direct bury cables (UF) and column 3 is nonmetalic conduit (PVC). This application falls into column 4

The advantage of going to the breaker is that the circuit will be dedicated and for lack of a better term, all of the electricity in the circuit will be available for you. If you tie into the load side of a GFCI receptacle it will still be 100% legal but you will have to share the power with other items.

Share this post


Link to post
Share on other sites

Is it worth it or not? That is the question. Go to your rental center and rent a trencher. Put it as deep as the trencher goes (usually about 3 ft. or so). This will cost you about $100. The wire will be another $100-$200, and then get an electrician quote. For a small job they will probably charge you a little more than usual. This will cost you at least $400.

I think this is the initial answer you were looking for. If you want to tackle it yourself, there is some good advise here, especially from the electricians here.

Share this post


Link to post
Share on other sites

BTW, frost does break wires, so make sure it is deep and loose.

Share this post


Link to post
Share on other sites

Roofer dude,

I'm just stating what it HAS TO BE, as in the minimum. The NEC tells you the minimum required. Heck, if you want to you could put it in rigid pipe, encase it in 4" of concrete and run 500MCM wire out there if you want to. That would be legal too.

Share this post


Link to post
Share on other sites

Didn't mean anything by it mnfishinguy. I know that you know your stuff and I'm sure it is well appreciated by many. smile

Share this post


Link to post
Share on other sites

I wouldn't say "many" wink It's an interesting book, I recomend it to anyone needs to go crazy. It would be nice if more of the codes "where across the board" but then agian, that's what they pay me for, is to know when to apply what rule to what situation.

Share this post


Link to post
Share on other sites

I wouldn't say "many" wink It's an interesting book, I recommend it to anyone needs to go crazy. It would be nice if more of the codes "where across the board" but then again, that's what they pay me for, is to know when to apply what rule to what situation.

I would like to have a dollar every time they say "shall and shall not" grin

Share this post


Link to post
Share on other sites

There can be other questions as well. Will you be running under an area where vehicles drive? If so, code is different.

Bob

Share this post


Link to post
Share on other sites

Roofer dude,

I'm just stating what it HAS TO BE, as in the minimum. The NEC tells you the minimum required. Heck, if you want to you could put it in rigid pipe, encase it in 4" of concrete and run 500MCM wire out there if you want to. That would be legal too.

I can't help but poke a little fun here.

It would be legal if the circuit components could handle the 500MCM. I'm thinking it would not be legal to use it to supply a 30A panel.

Bob

Share this post


Link to post
Share on other sites
Guest
This topic is now closed to further replies.
Sign in to follow this  
Followers 0



  • Posts

    • Why would they bother cutting a measly 8 to 10 trillion from the debt?   And why would they consult with a kook like Rand Paul?      
    • First, I am Christian and I'm not ashamed of it.  Second, the 1st amendment to our US Constitution guarantees that the government shall not make any laws respecting the establishment of religion or the free exercise thereof.    This means that the government is not permitted to endorse or decide for the people what religion, if any, the people will follow. At the same time, there is nothing in the law that declares that we the people are restricted from expressing our personal religious views or beliefs. Therefore, it is well within my rights to share my Christian views whenever I wish except I cannot use government property or my position as a representative of the government as a forum to do so.
    • Drum roll please................. The clear cut winner was the sinking radish seed by a 4-1 margin over the floaters. I even gave the floaters an extra day to pop up but they didn’t. I know come planting time I am going to check my radish seed this way. I also hear this works for tomato seed so that may be my next experiment but not till I am ready to start growing my tomatoes. Peppers come to mind as another seed to try out.   Now the radish I have seeded will not go to waste I saw a program where a guy plants radish and lets it grow to about three inches then cuts the top two and half inches off. He sells the tops to restaurants who use it on plates and also in sandwiches. You are suppose to be able to eat the tops at this stage and it tastes like radish... Kind of like eating sprouts but only eating the top of the new growth not the bottom...
    • Yep, I have noticed that too. That is a good thing to have in your back pocket in playoffs and you get caught in your zone for an icing or who knows what reason where you cannot switch lines OR just to have flexibility with matchups line vs line, but faceoff on one side vs the other.
    • Meh, his exacts words were " I tried to set myself on fire."   Setting yourself a blaze is fairly simple and effective if you want to be on fire.   I'll put him in the bat poop crazy, drama queen Zoloft category along with a former girlfriend.   You know, the one that chokes down a handful of Bayer and chases it with a fifth of vodka then proceeds to call 911 right after. Then everyone has to listen why, all the while there was no real danger.   
    • To be honest, I think of the cross as representing a burial site of a fallen soldier.  I don't necessarily even think religion when I look at the thing. In my opinion it is not even a religious symbol in that context. But that's just me.
    • The reversible plank is what they were carrying when I picked it up.  I've just been calling it carsiding because it's what most people are more familiar with.    I have that all stained and polyurethaned on the smooth side.  To me the bead side looks kind of dated.
    • Something else to keep in mind. When I was bow hunting I learned judging distance is not as easy as one might think. The bow I used was not super fast so judging a deer to be at 30 yards when it was really 40 yards would mean missing.    In my experience, we over-estimate distance sometimes by quite a lot on open areas such as open fields or on a lake. On an open area one doesn't have anything to provide a size reference so we tend to think objects are closer than they really are. Sometimes we can be off by quite a bit.   It works just the opposite in the forest where we have lots of references for size. Most of the time when a guy says he shot his deer from 50 yards it is probably a good bet that it was not quite that far. Personally, I don't like to get too close to anyone else. When on open water I rarely fish where others are. This can sometimes work against me as there is probably a reason for them being there. When ice fishing I try to stay 50 yards or more away from others. At the very least, I don't want to be close enough that our lines could become crossed when handling fish. 
    • Exactly.     We don't need to compete with Christians and their War on Xmas for the King Crybaby award.
    • Unfortunately he is still in the gene pool. He suffered non-life threatening 3rd degree burns to his back. 
  • Our Sponsors