How deep does the trench need to be? I believe that there is one depth for wire in conduit and one for just buriable wire?

I need to run 80 feet, will 12 gauge wire be enough? Just one outlet and a motion light.

Share this post


Link to post
Share on other sites

Need more information.

Are you going to be on a GFCI breaker or GFCI protected circuit or an a regular breaker?

If you are going to put it on a GFCI breaker and use UF wire the trench has to be NO LESS than 12 inches deep.

Share this post


Link to post
Share on other sites

When i ran a line out to my building it was a 20 amp with a seperate box with GFCI and they enclosed the wire in a tube and we made it 36". Of course we were running gas line also and that was in a seperate trench at 36"...so maybe thats why we put both at 36".

Share this post


Link to post
Share on other sites

As said, check your codes.

Where I live it has to be down 18in.... I would run it in pipe that way you can always

upgrade. Also a little more shovel prof. Make a map with locations on it.

If you are going to put spotlights in you fixture and a 80 foot run, you

better stay with 10ga. wire.

Share this post


Link to post
Share on other sites

Need more information.

Are you going to be on a GFCI breaker or GFCI protected circuit or an a regular breaker?

If you are going to put it on a GFCI breaker and use UF wire the trench has to be NO LESS than 12 inches deep.

Share this post


Link to post
Share on other sites

You better get right on it if you are planning to get it done yet this year. Depending on your soil type most times homeowners and do it yourselfers will use UF cable because of cost and ease of installation. Depending on where you picking the up from you may not need to add a GFCI receptacle or breaker. If the circuit is not GFCI protected already you will need to add either a GFCI breaker or GFCI receptacle. You will find breaker cost of $30.00 and receptacle cost $5.00.

If I was doing what you say it would be 12/2 UF w/ground direct buried and a GFCI receptacle.

UF Cable minimum of 24 inches. Unless covered by 2”-4” of concrete.

PVC Conduit minimum of 18 inches.

Share this post


Link to post
Share on other sites

fishingishot is definatly on the money. Any of those uses would be acceptable. But i would still looking into it further. As some city codes may differ.

Share this post


Link to post
Share on other sites

The NEC (National Electrical Code) article 300.5 states that;

Residential branch circuits rated 120 volts or less with GFCI protection and maximun overcurrent protection of 20 amps you need to be 12 inches deep.

You will need 18" if you are running under an airport or adjacent areas but not in your backyard. You will also need 18 inches if running UF wire in places that are not residential, but, and I repeat, article 300.5 states that for residential use, 120 volts or less and GFCI protected, 12 inches. You can get by with 6 inches deep if you want to put it under 2" or concrete if you want to.

In the residential column, the only places you need to be more than 12" is under streets, road and such or airports, neither of which fit into this particular project.

Thats the issue I have with the code book and not knowing how to read it. I've said it before and I'll say it again. Not all rules apply to all situations. What someones cousin did in their shed dosen't mean the same rules will apply to the bathroom in a church. Without knowing exactly what it says and how to read it, no advice is better than bad advice.

10 ga wire would not be the way to go for this application, heres why. You are allowed 3% voltage drop, by code. 12 ga UF wire will excede 3% at a 12 amp load. With 10 ga wire you will be at 3% with a full 20 amps.

Share this post


Link to post
Share on other sites

If I was doing what you say it would be 12/2 UF w/ground direct buried and a GFCI receptacle.

UF Cable minimum of 24 inches. Unless covered by 2”-4” of concrete.

PVC Conduit minimum of 18 inches.

Where are you getting your information? 18" for PVC is under driveways, not backyards. If you are looking at 300.5 look at column 4. Column 4 is for residential, column 1 is direct bury cables (UF) and column 3 is nonmetalic conduit (PVC). This application falls into column 4

The advantage of going to the breaker is that the circuit will be dedicated and for lack of a better term, all of the electricity in the circuit will be available for you. If you tie into the load side of a GFCI receptacle it will still be 100% legal but you will have to share the power with other items.

Share this post


Link to post
Share on other sites

Is it worth it or not? That is the question. Go to your rental center and rent a trencher. Put it as deep as the trencher goes (usually about 3 ft. or so). This will cost you about $100. The wire will be another $100-$200, and then get an electrician quote. For a small job they will probably charge you a little more than usual. This will cost you at least $400.

I think this is the initial answer you were looking for. If you want to tackle it yourself, there is some good advise here, especially from the electricians here.

Share this post


Link to post
Share on other sites

Roofer dude,

I'm just stating what it HAS TO BE, as in the minimum. The NEC tells you the minimum required. Heck, if you want to you could put it in rigid pipe, encase it in 4" of concrete and run 500MCM wire out there if you want to. That would be legal too.

Share this post


Link to post
Share on other sites

Didn't mean anything by it mnfishinguy. I know that you know your stuff and I'm sure it is well appreciated by many. smile

Share this post


Link to post
Share on other sites

I wouldn't say "many" wink It's an interesting book, I recomend it to anyone needs to go crazy. It would be nice if more of the codes "where across the board" but then agian, that's what they pay me for, is to know when to apply what rule to what situation.

Share this post


Link to post
Share on other sites

I wouldn't say "many" wink It's an interesting book, I recommend it to anyone needs to go crazy. It would be nice if more of the codes "where across the board" but then again, that's what they pay me for, is to know when to apply what rule to what situation.

I would like to have a dollar every time they say "shall and shall not" grin

Share this post


Link to post
Share on other sites

There can be other questions as well. Will you be running under an area where vehicles drive? If so, code is different.

Bob

Share this post


Link to post
Share on other sites

Roofer dude,

I'm just stating what it HAS TO BE, as in the minimum. The NEC tells you the minimum required. Heck, if you want to you could put it in rigid pipe, encase it in 4" of concrete and run 500MCM wire out there if you want to. That would be legal too.

I can't help but poke a little fun here.

It would be legal if the circuit components could handle the 500MCM. I'm thinking it would not be legal to use it to supply a 30A panel.

Bob

Share this post


Link to post
Share on other sites
Guest
This topic is now closed to further replies.
Sign in to follow this  
Followers 0



  • Posts

    • Where did you hear that food plots were to be banned?   I have seen about banning "feeding deer"  which I took to mean the classic set up a feeder and dump corn and alfalfa in it.     Jumping on areas immediately has been shown to be successful in preventing isolated cases from spreading and becoming endemic.   Once it becomes established in the herd, it seems as if controlling it is no longer possible.   It also seems as if CWD is fairly hard to catch for a deer, or else it would be all over everywhere and all the deer in an area like Dane county would have it.    Oh, and the infected deer could have come from a deer farm, or from Iowa where it has been detected in the county bordering MN on the SE.    
    • I wouldn't call myself wealthy, but I've made good life choices that have enabled me to buy my own land.  Still pack my own lunch and watch for sales at the grocery store.  I don't own land in SE MN, I own land in northern MN.  The reason I am concerned is that this will serve as a template for herd control tactics in other parts of MN.  Understand that the game management agencies have conferences where they talk about managing hunters.  You don't have to look any further than the work of Dr. Gary Alt in Pennsylvania.    I can't put my finger on exactly what is going on with the results the DNR has presented.  Were the samples snuck in by a nefarious actor?  I wouldn't rule it out.  Was the disease always here and just finally discovered?  I don't see why not.  Is there a unique environmental reason that CWD hasn't gotten a broad foothold here?  It's possible.    If the agency had some credibility going into this, I'd be on board pounding kool aid myself, but they don't.  So color me skeptical.  None of the WI border counties along zone 3 have CWD according to this map.  However, Burnett and Polk do and there is no monitoring on our side up there.  Can a scientist explain that to me?  Because the geographic barriers up there are non-existent compared to  the Mississippi River along zone 3.       
    • I made the decision to replace the pump every few years rather than the carpet.
    • On my aluminum skid house I've been using thread cutting stainless steel screws from Fastenal
    • There might be a pleasant surprise in the works.   In the meantime, it is entertaining to watch anyway....      
    • Huh---Guess you must have the butthurt.
    • You are cooking it before you eat it right? I've only heard people using Cure when using dehydrators or may be for jerky when using burger. I have never used the stuff but don't like or make dehydrated jerky.   Seem to still be alive!
    • Creepworm, I am somewhat angry.  The reason it's fool hardy to consider food plots any more threat than a farm field is that the intentions of the planter don't change the flavor of the forage.  A food plot is no more attractive than the edge of a 160 acre bean field that meets a fence line, swamp edge, or grove.     Now imagine there are no farm fields or food plots at all, not even a decent yielding apple tree.  Deer will still communicate via scrape trees and licking branches during the rut.  If the current belief is that the prions spread via saliva, what's to stop wild deer from licking a branch that an infected buck has licked?  What's to stop a buck from rubbing their face all over a contaminated branch?    My fear is that lots of deer are going to be slaughtered in an area that just happens to have been a hot target for eradication before CWD was found.  I'm also worried we're going to get all kinds of bad rules imposed that won't do squat to actually stop the spread if the disease is actually in MN.  I'm worried we'll lose a critical habitat tool that allows us in harsh winter kill areas to help the deer make it through winter (food plots).    It'd be interesting to watch the DNR try to ban food plots.  Good luck defining what is and is not a food plot. 
    • Don't know how they got there.  Maybe they got confused with CWD and wandered up from Iowa.   Or maybe there are a few more but they didn't happen to get shot or didn't get tested.     So, you are a wealthy land owner?  Is the land in 348?     Sure, you are free to question the DNR.   I never said you weren't.   And you, so far as I know, are free to refuse to cooperate with the program to control CWD.   As I have said, that is exactly the response of the land owners in Wisconsin that I recall from back in the day.     However I am curious.   Are you accusing the DNR of planting or fabricating this instance of cwd for some nefarious purpose, like killing most of the deer in that area for unknown reasons?   Or do you just think that these were the only two sick deer and everything will be fine without any action? 
    • Nice product.  Would work great with my Lindell Ice Rigs....
  • Our Sponsors