Don Julio Posted September 16, 2014 Share Posted September 16, 2014 Anyone have an answer for why you now need a 100# propane tank to run a procom ceramic ventless heater? I've ran them in my fish house for 10 years. I went to order one to use as a backup in my new Yetti and was told by Northern Tool I must have the larger tank for it to work properly. Maybe since they are all duel fuel they won't work on a 20# tank. Any ideas? Quote Link to comment Share on other sites More sharing options...
leech~~ Posted September 16, 2014 Share Posted September 16, 2014 They make more money selling 100#'s? Not sure with the right regulator why any size tank wouldn't work? Quote Link to comment Share on other sites More sharing options...
Hawg Posted September 16, 2014 Share Posted September 16, 2014 Sounds crazy to me, the regulator decides what the pressure is. Quote Link to comment Share on other sites More sharing options...
Gus Posted September 16, 2014 Share Posted September 16, 2014 My guess is it has more to do with delivering volume. I had a garage convection heater that the manual said minimum 100#. I ran it off a 20#, and while it ran, it never burned clean and was downright dangerous. When running off a 100# tank, it DID run much cleaner. I ended up getting a smaller BTU convection heater that the manual said was ok on 20# tank. Much happier with the way it runs. I'm not a propane expert, but I don't think they would put it in the manual unless there was some reason for the bigger tank. And from my experience, there is a difference. Quote Link to comment Share on other sites More sharing options...
Hawg Posted September 16, 2014 Share Posted September 16, 2014 Doesn't the regulator control volume? I sure thought it did. Quote Link to comment Share on other sites More sharing options...
LittleHuck Posted September 17, 2014 Share Posted September 17, 2014 Regulators control pressure, not volume. What's probably happening is there is too much of a pressure drop with the 20lb, especially if it was an exchanged cylinder, they're only filled to 60% capacity. With the 100lb, there's 5 times the liquid propane vs a full (80%) 20 pounder, therefore less pressure drop when in use. I deliver propane for a living, so I know a thing or two about it. Quote Link to comment Share on other sites More sharing options...
leech~~ Posted September 17, 2014 Share Posted September 17, 2014 Regulators control pressure, not volume. What's probably happening is there is too much of a pressure drop with the 20lb, especially if it was an exchanged cylinder, they're only filled to 60% capacity. With the 100lb, there's 5 times the liquid propane vs a full (80%) 20 pounder, therefore less pressure drop when in use. I deliver propane for a living, so I know a thing or two about it. So, your the guy under filling everyone's tanks!!! Quote Link to comment Share on other sites More sharing options...
LittleHuck Posted September 17, 2014 Share Posted September 17, 2014 Lol, not me! Luckily for me, the co-op I work for doesn't have a cylinder filling program, also we were one of the very few co-op's that didn't have to ration propane last winter for home heat or ag use, not to mention one of the cheapest. $4.00/gallon was our highest cash price, and that only lasted for 3 days, then back to $3.50 for a few weeks before falling further. Quote Link to comment Share on other sites More sharing options...