natural gas garage heater installation


Bigbartguy

Question

hi folks

I'm thinking of installing a nat gas garage heater. I'm wondering if it's acceptable to use the flexible copper tubing out to the garage?

they used this same copper tubing to my fireplace, dryer and also the line marked 'main' which looks to be my main line coming into the home. The pipe to the main furnace is the black iron pipe. Just wondering if outside(garage) installations require the black pipe or can I use copper? It would run directly from the basement into the garage, along the garage wall to the corner.

thanks!

ps-I've ran tubing before, for fireplace - just not sure if this would require something else?

Link to comment
Share on other sites

4 answers to this question

Recommended Posts

  • 0

As long as it's supported and not run in a place likely to get damaged, you should be OK. Need to size it correctly, if it's a long run, you may be better off running a 2# system to the garage and then a regulator at the unit heater. Call your inspector and ask.

PS. I'm a plumbing/HVAC inspector in the metro area, but not where you live.

Link to comment
Share on other sites