Empire direct vent install question


JSK76

Recommended Posts

I'm in the process of installing and Empire DV-215 vented wall heater and can't find out any info on if I can insulate with spray foam between the hole in my wall and the air inlet tube. My guess is it should be safe to do since its got fresh outside air coming into the heater and that should make it not get too hot.

This is a pic from the outside of the house. The part I'm talking about is the space between the wood and the long aluminum pipe (haven't cut the pipe to size yet) the exhaust runs in another pipe inside this one.full-26462-25597-image.jpg

Link to comment
Share on other sites

I will disagree with the last two posters. If you look at your install manual it calls for a minimum 6 1/4" opening. The outside air inlet pipe is 5" in diameter. The back side of the mounting bracket also acts as wall thimble. If the manual requires minimum 6 1/4" clerance, than spray foaming around the pipe would be against their requirements. I have installed at least 10 of these units in the past. I wouldn't worry about the extra 3/4" of air space, it's obviously required for a reason.....FIRE. A simple silicone caulking job around the outside vent termination should take care of any air infiltration.

Link to comment
Share on other sites

Thermos is right, if you ever go out side by your exhaust vent it is so hot that you cant touch it.So Im sure even the outer fresh air pipe is hot. I guess wouldnt recommend insulating that close, but mine was that way when I got it and havent had any problems but I guess its a possability.

Link to comment
Share on other sites

like stated above. Its not a good to put any sort of insulation on or around the pipe. Any direnct vent heater , fireplace, ect. needs to have a air gap between pipe and combustables. Silicone the outside termination kit to whatever siding you have and you should not have any cold air draft coming into the house.

Link to comment
Share on other sites

I agree on not to insulate. There should be 1" clearance. You could probably caulk the gap with a hi temp RTV silicone for air. You won't loose much heat out of that hole. At times your house will become hot you may end up cracking a window. So that little gap isn't going to make much difference. IMHO

Link to comment
Share on other sites

Join the conversation

You can post now ↓↓↓ or ask your question and then register. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.



×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Privacy Policy. We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.