Another question beyond my meter socket


jentz

Recommended Posts

Off my outdoor breaker box. I ran 10-3 underground to a post and I want to install 2 recepticals, each off a seperate 15A breaker.Question Can I split the UF 10-3 and use the black lead for 1 box then run the red to the next box? The boxes are stacked one ontop of the other lowest is 14 inches above grade then a 4 inch seperation.If I can how do I strip the gray shielding??

Question 2 my meter box and breaker are mounted on 1 4X4 back to back can I drill out the backs of each box,Where there are no knockouts to make my main 4/0-4/0-2/0 connection threw conduit?

Thank you mnfishinguy for your last answer.I did call the inspecter with this question,I got a answer machine and who knows when he may, or not call back.

Link to comment
Share on other sites

Can't be much different than a square meter socket mounted on a round power line pole. But, if it doesn't work for your application, that's cool.

I believe there are connectors to connect two boxes together, too, so you wouldn't have to deal with that 4" separation.

Link to comment
Share on other sites

Off my outdoor breaker box. I ran 10-3 underground to a post and I want to install 2 recepticals, each off a seperate 15A breaker.Question Can I split the UF 10-3 and use the black lead for 1 box then run the red to the next box? The boxes are stacked one ontop of the other lowest is 14 inches above grade then a 4 inch seperation.If I can how do I strip the gray shielding??

Yeah, I think you could but two circuits on a 3-wire cable means a common neutral circuit. For common neutral circuits I believe you need to use a common trip/two pole breaker, or two separate breakers with an actuator tie kit.

This for two reasons -

1. Makes sure the cable is dead because if just one side were to trip someone who didn't actually check might assume the whole cable/circuit was dead.

2. Forces the breakers to be on opposite legs of the panel so that the neutral sees only the difference of the two circuit loads rather than the sum, if they're on the same leg, which could/would be dangerous.

Also, IMO, since you're running 10ga you might just as well use 20A breaker.

Link to comment
Share on other sites

There would be less voltage drop. Whether or not it ends up being a meaningful factor depends, of course, on the length of the run and load.
Exactly I did check voltage drop,I used 97ft.of wire, breaker to recepticals. I did use a two pole 15A breaker.I also checked other neighbors boxes.Sewer was recently installed and those electricans drilled out meter boxes and shutoff boxes,and one outdoor breaker box.They were existing and they made the same back to back drilled out connections I just did.The inspecter never called back, so I went knocking on doors asking to open their boxes.All those boxes were installed and inspected so I figure I am ok.

Thanks for the help.

I like to think I am abit more cautious and gather more information than the average DIYer!

Link to comment
Share on other sites

Join the conversation

You can post now ↓↓↓ or ask your question and then register. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.



×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Privacy Policy. We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.