      Fluid forum view allows members only to get right to the meat of this community; the topics. You can toggle between your preferred forum view just below to the left on the main forum entrance. You will see three icons. Try them out and see what you prefer.   Fluid view allows you, if you are a signed up member, to see the newest topic posts in either all forums (select none or all) or in just your favorite forums (select the ones you want to see when you come to Fishing Minnesota). It keeps and in real time with respect to Topic posts and lets YOU SELECT YOUR FAVORITE FORUMS. It can make things fun and easy. This is especially true for less experienced visitors raised on social media. If you, as a members want more specific topics, you can even select a single forum to view. Let us take a look at fluid view in action. We will then break it down and explain how it works in more detail.   The video shows the topic list and the forum filter box. As you can see, it is easy to change the topic list by changing the selected forums. This view replaces the traditional list of categories and forums.   Of course, members only can change the view to better suit your way of browsing.   You will notice a “grid” option. We have moved the grid forum theme setting into the main forum settings. This makes it an option for members only to choose. This screenshot also shows the removal of the forum breadcrumb in fluid view mode. Fluid view remembers your last forum selection so you don’t lose your place when you go back to the listing. The benefit of this feature is easy to see. It removes a potential barrier of entry for members only. It puts the spotlight on topics themselves, and not the hierarchical forum structure. You as a member will enjoy viewing many forums at once and switching between them without leaving the page. We hope that fluid view, the new functionality is an asset that you enjoy .
Sign in to follow this  
bhs91

24 volt system

Recommended Posts

I just bought a 80 minn kota vector and need to do a little 24 volt wiring??? The manual says I need a 60 amp manual reset circuit breaker, the guy at Gander said if put a 50 amp (auto reset) on each of my "hot" lines, that will be fine. He is a good guy and I trust him, but is he right???

Thanks,

BHS

Share this post


Link to post
Share on other sites

I wouldn't put a 50 amp on each line 100 amps is a very large amount of current to run to a trolling motor, if the manual says 60 max then get 2 30amp breakers one for each battery.

Most peoples homes only have 100 amp service and would you want 100 amps to every outlet?

Are you wiring each battery to the plug? or you wiring the batteries in series with only 2 wires to the plug?

with the 2nd question then a 50 or 60 amp breaker would be fine, with the first question then you would want to halve the current from each battery, hence the 30 amp per battery.

Share this post


Link to post
Share on other sites

I am in the midst of converting my 12 volt system to 24 volt. I asked at a dealership about circuit breaker and he said one 50 amp is needed.

I have a question about charging. Since the trolling batteries are connected in 24 volt can I get away with a one bank charger to charge both batteries or do I need a charger for each battery? If I do need separate chargers for each battery do I need to disconnect one battery so it isn't in 24 volt mode?

Share this post


Link to post
Share on other sites

You could use a one bank/single charger to do both batteries if it is a 24V charger, or a single 12V charger if you can put up with charging only one battery at a time.

You do not need to disconnect the wire between batteries when charging them regardless if using a single charger or a multibank unit. All you have to do is connect to just one battery per charger/bank and observe the correct polarity when making your charger to battery connections.

Share this post


Link to post
Share on other sites

I have couple other questions. First, my conversion to 24 volt was going to have the second battery in the front storage deck. A person said that I would be losing a lot of power because of the length of wire needed to connect the two batteries. There is about 10 feet of 8 gauge wire connecting the two batteries. How much power would I lose? Would the power loss be noticeable in the speed or the amount of charge being used? I am planning on putting on a MK Maxxum 70 on.

My other question, if for some reason I could fit a battery in the rear deck closer to the other one I might need to use a smaller battery that might not be deep cycle. Would this affect the amount of juice being used being smaller and non-deep cycle compared to the larger one?

Share this post


Link to post
Share on other sites

For max run time and power both batteries need to be the same size. I always go biggest I can fit, in my case thats a non issue so I run 29 or 31 series. Deep cycle is a must to get any amount of decent run time. Not sure on power loss due to the longer length of run but sounds like a pain to me. I run a 3 bank in my boat, not needed but price was right. I know Optimas are expensive but in your case may be worth it for the compact size and quality. You can buy them in a 24 Volt version but not sure on the dimentions of it.

Share this post


Link to post
Share on other sites

There is alway some loss in wiring. Without knowing the specifics of current draw, the exact amount is only a guess.

One must consider the complete circuit length because not only is the wire between the batteries a factor, so are the other two pieces connecting the batteries to the motor.

Just for an example, 40ft of 8ga wiring carrying 20A current will have a voltage drop of about 1/2 volt. That's about 2% in a 24-volt system.

Considering the same system, if the current is 40A, the voltage drop doubles to just over 1 volt. This is still less than 5% voltage drop in the wiring.

Going to 6ga wiring would cut those losses by roughly 35%. If you must get every last minute and every last ounce of thrust 6ga would be an option.

If you generally need to run the trolling motor pretty hard, as in near full power, I might consider the 6ga more strongly. However, if your use is not so severe, 8ga should be fine with no appreciable loss in performance.

I wouldn't compromise the battery size because of the wiring you have. If you do anything different, keep the location where big batteries will fit and upgrade to 6ga wiring.

Share this post


Link to post
Share on other sites

Thanks for the info. I found a way to get all three batteries in one compartment. Luckily, I haven't mounted anything or drilled any holes. The only problem I have now is if I get a three bank on board charger the only place I can mount it is on the floor of the rear compartment. Is this ok? I was talking to an associate at Gander and he said that Minn Kota is the only one that he knew of that claims to be 100% water proof so if the charger is in water it will still work. He said MK tests their chargers underwater so they can make this claim. Any other brands make this claim?

Share this post


Link to post
Share on other sites

My Pro Mariners mounted under the sink, I know its been wet many times and works fine, I can't find the book on it to see what it says. If you mount it on the floor in a compartment don't cover it with gear, in our muskie boat that chargers in the battery compartment and we always leave the hatch open a little for air flow to prevent overheating.

Share this post


Link to post
Share on other sites

Correct me if I'm wrong when hooking up the two batteries to create 24 volts. Don't you hook up positive from one to the negative of the other and negative to positive? Both jumper wires were hot(which tells me I'm doing something wrong) and I got a spark when I hooked the negative to positive to complete it. I didn't damage the batteries did I?

I connected the circuit breaker to the trolling motor lead positive wire.

Share this post


Link to post
Share on other sites

Correct me if I'm wrong when hooking up the two batteries to create 24 volts. Don't you hook up positive from one to the negative of the other and negative to positive? Both jumper wires were hot

You only use 1 jumper, not 2 jumpers. The POS on 1 battery goes to the trolling motor and has the circuit breaker on it. The NEG from the OTHER BATTERY goes to the trolling motor. You use 1 jumper to connect the open NEG on the 1st battery to the open POS on the 2nd battery.

The other way to make a 24 volt connection is for the POS and NEG from each battery to go to a power port, and to have the 24 volt jumper connection made inside the plug on the trolling motor wires.

Both methods work but I think the first method with 1 jumper wire is easier.

Share this post


Link to post
Share on other sites

Just to make sure I read you correctly, The trolling motor leads +/- is connected to battery 1. Then I took a jumper wire and added it to the + of battery 1 and connected it to the negative of battery 2. This leaves the + on battery 2 with nothing connected to it.

Share this post


Link to post
Share on other sites

Got it. Ok, I'm an [PoorWordUsage]. I have a trojan battery and I didn't realize I had two connections on the positive. blush

Thanks for every ones help!! Now all I have to do is buy the motor.

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

Sign in to follow this  



  • Posts

    • anybody know what it is?
    • I've been finding a few hens, but nothing like last year (which was great for me).  Here's one that was just shy of ten pounds sitting next to my daughter.
    • You may as well paddle a green kiddie pool around.  Might find one for 50 cents if you look a little. Um, yeah, I've actually seen it done. 
    • Good move!  I'm sure they are thankful! I might've made an offer if I'd seen this before but they'll probably be better used in the organization that received them. Sorry the hear your hunting days are over.
    • There is no way Koivu doesn't get more term and $$ in free agency, not a lot more but he gets more. Marleau is trending down and got more money, Hansel got 750 less and is not in the same league as Koivu. I was hoping for something like 4.5 or 5 but what he got at 2 years is very reasonable. He is a lifelong wild, our captain and a great player, we have no immediate replacement, he makes our team better for the next 3 years be it 1/2/3 center. This isn't something to get upset about, scandella trade sure, aging parise sure but that had to be done, not getting a young center sure but that can sometimes be out of our control because it takes two teams to trade. I get it people are bitter about last year but what fan base isn't bitter about this or that? 
    • I ran 10 gauge wire from my shore or generator feeder to my converter.  Way over kill for a 2000 watt generator but if you ever take it camping or run it off a 3k in the summer it's nice to be wired for the extra wattage.  10 feet of 10 gauge really isn't that much money on the whole project... nice thing about running your inverter directly from the battery and splitting a couple outlets is they are always ready to go.  Just hit the switch on the inverter and you don't have to mess with unplugging and plugging in strings of 110 outlets.  Behind my tv the bottom outlet runs of the Genny and the top runs of the inverter.  Nice thing is if I ever wanted to run the whole 110 system off the inverter I can just run a 6 inch cord with a male plug on each end out the top outlet and into the bottom and power the whole house.
    • This looks like it will work to me. I had thought of doing something similar when I was thinking of going with the inverter, seperate 12v fuse block and onboard charger. Would have wired a "hot" outlet direct from generator. Then ran a piece of romex with a male plug wired onto it and tied the 110v into that. then I could have either plugged that into the "hot" outlet along with the onboard charger, when the generator was running. Or I could have plugged it into the inverter when needing to run off battery power.
    • never been there, have to go!!!   off 10 right???   or where?? thanks!!
    • Thanks everyone for the replies. I am planning to go with the ac/dc distribution panel with built in converter and charger. Then adding an automatic transfer switch, and an inverter. I m going to bring  the exterior generator outlet directly into a gfci outlet box. Then wiring the transfer switch as follows... To the NO(normally open) terminals I will wire either a piece of 14ga romex with a male plug wired on the other end, or just get a cord of the correct size with the plug on it, which will plug into the "hot" gfci outlet being fed by the generator. I will do the same at the NC(normally closed) terminals, which can be plugged into the inverter. Then from the transfer switch output I will wire a piece of romex with a female plug, or correct size cord with same. From the main terminals on the 110v side of the distribution panel I will wire of piece of romex or cord with a male plug on it. That can then be plugged into the female plug coming out of the transfer switch. I figure wiring it that way gives me the option of bypassing the transfer switch and plugging the distribution panel directly into the "hot" gfci outlet from the generator if the transfer switch should fail. The transfer switch should feed the output from the NO terminals as long as they have power to them. If they lose power, i.e. turning the generator off, then the NO terminal close and it switches the NC terminals open and feeds the output from those, which would be the inverter in this case.   I had been told by one of the places that sells fish house materials that I couldn't wire an inverter in with one of their WFCO panels. I knew there was a way so I thank you guys for making me think about it a little more. I think this set up will give me exactly what I'm looking for. I plan on running a Honda 2000W generator, and then two 31 series AGM batteries wired in paralell. Will run the generator during the day when convenient, but also want the ability to "run and gun" more when conditions allow without needing to set up the generator every time just to power a couple small AC items.   Anyone have any experience with the automatic transfer switches? Go Power brand seems to have good reviews. Same with distribution panels. 2 I see the most are the WFCO and the Progressive Dynamics. YettiStyle, what is it that you prefer about the Progressive Dynamics panel? Better quality? Easier connections? etc...   Thanks again to everyone!
    • Yes, if he's coming back on his own don't screw with adding something new he's not use too. 