chasineyes

Power for Heater

11 posts in this topic

I'm going to be installing a 45,000 Hot Dawg heater in my garage and was wondering what type of power that needs. Can I just run off of my regular garage power or does it need a dedicated power supply? OR could I tap into my furnace 20amp line dedicated line?

Share this post


Link to post
Share on other sites

It should be on its own circuit. 15 amp breaker, 12/2 wire to a switch mounted on the wall next to the heater, from there 12/2 in flex conduit to the heater. Can you fish the wire from the panel to the switch or will you need to run conduit? Question, do you have a panel inside the garage or are you coming from the house?

Share this post


Link to post
Share on other sites

Unfortunately I'm coming from the other side of the house in the basement with solid floor joist. What I may do is just cut a slot in the rock and run 2 dedicated wires, one for the heater and one for the garage. Currently I have the garage with a freezer and outside lights on one circuit. Suffice to say when I power up the saw, lights, vac. I tend to flip the circuit. I'm thinking lets just make the mess and do it right.

Share this post


Link to post
Share on other sites

What size wire is run out to the garage now?

If your going to make a mess you might as well run 220 and a new panel in the garage.

"What I may do is just cut a slot in the rock and run 2 dedicated wires"

Not sure exactly what you mean there but before you get replies saying its not a good idea to do that, we can suggest ways to get that done and be code. Without seeing what you have its hard to say.

Share this post


Link to post
Share on other sites

After looking at my circuits, why would my sump pump need a designated 20 amps. and my furnace 15? I can honestly say it has never been used in our 6 years. Very sandy/all sand soil. Since the mechanical room butts up against the garage, I think I'll run a line from the box for the sump to the heater. This is going to be a very light usage operation in the winter, not a full-blown shop like I wish I could have. By cutting a slot, I trimed in with oak paneling along my I-beam that runs the length of the room. What I was thinking was cutting 6" wide slot out of the paneling and laying in the wire then gluing a new panel back over the cut portion.

Share this post


Link to post
Share on other sites

Call your building inspector. You can still do this yourself, just get the correct info and have it documented.

Share this post


Link to post
Share on other sites

flex conduit

Frank, your killing me here! grin If your going to run it in flex you might as well just pull MC cable and eliminate a step. Flex and MC have their place in this world but it's best kept hidden 'cause there is no way to make it pretty. Remember, there is a reason that while flexable metalic conduit and MC cable are U.L. listed and legal to use, there are many municipalities and states that severily restrict their usage. I personally hate both flex and MC but then again I might be biased since I get paid to run pretty conduit.

OK, if your going to pull 12/2 wire you might as well put it on a 20 amp breaker. To be legal this receptacle needs to be a GFCI unless its going to be dedicated for the heater then it needs to be a single (not a duplex) receptacle.

Share this post


Link to post
Share on other sites

I read you are thinking of running a "line" under some paneling and gluing a cover back on? If you plan on using Romex (NMB) you will have to protect the wire from pysical damage by covering it with a nail plate at least 1/16th" thick. This is to protect someone who dosen't know it's there from driving a nail or screw into it. This does not apply if the wire will be at least 1.25 inches back from the surface. Article 334.15 (B) and 300.4(A)(1) and (2) will give you more guidance on this depending on your exact situation.

Share this post


Link to post
Share on other sites

Flex conduit is a beautiful thing and would compliment your conduit! laugh

I was assuming the Heater did not have a power cord. Therefore the flex conduit from the switch to the heater with no receptacle. Thanks btw for the reply and since your looking, is it or is it not code to have a device like that on a switch?

As far as running Romex behind the paneling, thats fine if you use the nail plates and as long as your drilling the studs keeping the 1.25" from the outside of the stud and running the Romex through it. Otherwise no, you can't just cut a channel in the paneling and run the wire in that.

Share this post


Link to post
Share on other sites

A rule of thumb on disconects. If it has a motor it must have a switch to turn if off for servicing. For a cord and plug connected appliance the plug in counts as the disconnect. Again, that statement does NOT cover 100% of every application out there, but it's a [PoorWordUsage] good reference.

For a hardwire installation I'd go with sealtite instead of flex. It looks alot nicer.

If a guy does do a hardwire installation here is one thing to remember. Run the wire inside the wall to a box. Anybody can do that.

Most guys make a hole in a blank cover for the whip (sealtite, flex or S.O. cord) attach the whip to the cover and splice it up (inside the box) and install the cover. You can't do that. You can't come out of the cover of a box. The correct way to do it is to install an extension ring and come out of the ring and have an unmolested cover on the ring. I'll admit it dosen't look as nice this way but it's the right way to do it.

Share this post


Link to post
Share on other sites

It should be on its own circuit. 15 amp breaker, 12/2 wire to a switch mounted on the wall next to the heater, from there 12/2 in flex conduit to the heater. Can you fish the wire from the panel to the switch or will you need to run conduit? Question, do you have a panel inside the garage or are you coming from the house?

Why 12ga for a 15A circuit?

Bob

Share this post


Link to post
Share on other sites
Guest
This topic is now closed to further replies.
Sign in to follow this  
Followers 0



  • Posts

    • i'll come hell ya leech!!!!!!!!!!!
    • Bureaucrate-   Correctly me if I'm wrong, weren't you a huge advocate against AIS lawd and allowing the DNR to pull over fishermen and boats for an inspection? But you are okay with them pulling over deer hunters?    Sounds like anything they do, you are against. If they said black, you'd say white...
    • The 2016 Libertarian Party is Starting! Started by Big Dave2, April 12, 2015   Is this post even relative anymore or has it ever really been? May as well just delete it and save some site Band width!
    • Same circuit as the freezer?!! Oh no no no......!!! They kick in at the same time, and  *TRIP* Always have the pump on a separate circuit!!  As mentioned, GFCI is what code calls for, but sometimes dampness will pop one, rare, but I've seen it happen. I nixed the GFCI on mine when I ran a separate circuit for just the pump. That should solve your problem. 
    • I am from Richland Center.
      I have 2 2500 stradics in dis-repair.
      Both bales refuse to return to closed.
      Heard it may be simple as a spring.
      I am kinda cheap….if costs a lot to fix i will buy new reel. Anyone know somewhat local repair person that is reasonable?
    • Well you can't drink all day if you don't start in the morning.  
    • Another one thawing.  made this one for my nephew but will keep it for me. So will have another one in the brine in a couple days. 
    • It's a little early to be hitting the bottle don't you think?  Believe in Trump and you'll feel better.
    • Ok I'll save you from dying. Where can i pick it up? 
    • I use to work on all aluminum body fire trucks.  The only screw, bolt, washer, or nut that we would use was stainless steel as the by using anything else will allow electrolysis to start from dissimilar metals and corrode.  Only problem was the strength of the SS is not as high as regular steel.  Also if you are using SS, i would only use bees wax as a lube.  I use to buy it in a block, and just rub the threads on the screw before putting in the hole.  If you don't, you may find that the threads gall up and strip out.  Then you have issues cause it can be tough to drill out a broken SS screw.  If you have a bunch to do, i found that a combination drill/tap was very useful.  It will drill the hole and tap at one shot.  Here is what they look like.  Good luck. http://www.graybar.com/store/en/gb/combination-drill-tap-bits-22082167?cm_mmc=pla:google-_-googleshopping-_-gb5349-_-22082167&utm_source=google&utm_term=&utm_campaign=Graybar>PLA>Category&utm_medium=cpc&utm_content=fto6JW9w|pcrid|49843833890|pkw||pmt|&gclid=CPzt0MP72tACFYKSfgodC4MH_g
  • Our Sponsors