      Fluid forum view allows members only to get right to the meat of this community; the topics. You can toggle between your preferred forum view just below to the left on the main forum entrance. You will see three icons. Try them out and see what you prefer.   Fluid view allows you, if you are a signed up member, to see the newest topic posts in either all forums (select none or all) or in just your favorite forums (select the ones you want to see when you come to Fishing Minnesota). It keeps and in real time with respect to Topic posts and lets YOU SELECT YOUR FAVORITE FORUMS. It can make things fun and easy. This is especially true for less experienced visitors raised on social media. If you, as a members want more specific topics, you can even select a single forum to view. Let us take a look at fluid view in action. We will then break it down and explain how it works in more detail.   The video shows the topic list and the forum filter box. As you can see, it is easy to change the topic list by changing the selected forums. This view replaces the traditional list of categories and forums.   Of course, members only can change the view to better suit your way of browsing.   You will notice a “grid” option. We have moved the grid forum theme setting into the main forum settings. This makes it an option for members only to choose. This screenshot also shows the removal of the forum breadcrumb in fluid view mode. Fluid view remembers your last forum selection so you don’t lose your place when you go back to the listing. The benefit of this feature is easy to see. It removes a potential barrier of entry for members only. It puts the spotlight on topics themselves, and not the hierarchical forum structure. You as a member will enjoy viewing many forums at once and switching between them without leaving the page. We hope that fluid view, the new functionality is an asset that you enjoy .
Sign in to follow this  
TKO_PUNCH

Electric Help!

Recommended Posts

Hello to all,

I need some emergency help with electricity to my hot water heater. I moved my water heater fuse box this weekend and now I do not have hot water. I checked the voltage coming into the water heater fuse box and that is fine but there is no voltage going to the water heater.

I removed the fuses and I had continuity on one fuse but the other one did not. I replaced the bad fuse with the new one. When I turned power back on, I tripped the breaker at the main fuse box and both fuses were still good. I then reset the main breaker and then I blew the fuse at the water heater breaker box.

On the fuse box to the water heater are line and load terminals. Which one is which? Black goes to what and white goes to what? I know both wires carry load but am wondering if the two got hooked up backwards.

I currently have the black wires hooked up to the load and the white wires hooked up to the line terminals.

Share this post


Link to post
Share on other sites

I was just talking with our Maintence guy and he said you cannot get the wires backwards as the both carry power. As long as I have both black wires to the load and both white wires to the line I should be fine.

He did say I have a bad heater element.

Anyone agree with this as I'm going to take a half day off work to change this.

Here is what he told me to do:

1) shut off the main water and open all the faucets.

2) Drain the water from the water tank

3) Remove the heating element

4) clean out all the sludge

5) replace the heating element

6) turn water back on

7) run water to get out all the air

8) after the water is flowing freely turn the power back on

Is this correct as I only have a few hours before I try this.

Share this post


Link to post
Share on other sites

I would beg to differ with the bad element diagnosis. A heating element will typically open when it goes bad, which means it no longer will have continuity. I also believe the elements are encased in non-conductive material and so they are not likely to short-circuit.

You say black and white wires. First if you have a black and white wire coming from the supply, and the white wire has not been properly marked as a hot wire per NEC regulations then you already have a system that was not properly wired.

The load side of the fuse box you refer to should be supplied by 220vac coming from a double-pole circuit breaker. Wires from the fuse box should carry the 220vac power to the top thermostat in the water heater. If these are crossed they may be the cause of your short-circuit. Without knowing what has been disconnected or what was improperly marked in your supply circuit, it is nearly impossible to explain precisely what needs to be done without putting you in harm's way.

Bob

Share this post


Link to post
Share on other sites

Obviously you have some wires crossed. Call a licensed Electrician before you burn your house down. If you're not sure what's wrong you probably shouldn't be messing with this.

Share this post


Link to post
Share on other sites

Well, I got home and the 1st thing I did with the power disconnected was remove the wires from the thermostate and elements. I had continuity to all. I then call an electical contractor and he said to disconnect the wires on top of the water heater that connect from the fuse box to the thermostat. Then to seperate all wires so there is no contact between them and install new fuses. If I hold power up to that point then there is an issue with the element or thermostat.

I them applied power to the fuse box without the fuses installed and it held power just fine. I turned off power, installed the new fuses and then applied power. BLOWN FUSE!

The contractor will be out this afternoon as I'm now beyond my comfort level. I'll post what happens after.

Share this post


Link to post
Share on other sites

I currently have the black wires hooked up to the load and the white wires hooked up to the line terminals.

This was my problem: 2 blacks to the load and 2 whites to the line doesn't work.

1 black to the load, 1 white to the load, 1 black to the line and 1 white to the line. Works just fine now.

Thanks to all for the advice.

Share this post


Link to post
Share on other sites

As I suspected, the wires are not properly marked. That white wire from the supply (load side) should be marked so it doesn't get confused with a grounded conductor. This is a very important code requirement. You can use black or red electrical tape to color the insulation or magic marker will work too. Just don't have the power on while you are fixing this. Remember to do both ends.

The wires from the fuse box to the heater should also be done the same way.

Bob

Share this post


Link to post
Share on other sites

As long as I have both black wires to the load and both white wires to the line I should be fine.

I caught that right. Bad things could have happened with that one. Like Bob T said, if your still using a white colored wire it's not legal. It must be permanenty reidentified. ONLY a grounded conductor can be white or gray in color.

Share this post


Link to post
Share on other sites

I now have the white "hot" wire marked with black tape. The electrical contractor who came out was kind of shocked that it passed inspection. His quote to me was "why do they make codes if they're not going to enforce them"

It is correct now!

Thanks again for all the help

Share this post


Link to post
Share on other sites
Guest
This topic is now closed to further replies.
Sign in to follow this  



  • Posts

    • This furnace has 2 pipes. The larger pipe about 4" is the air intake is supported through ring #29. The smaller pipe inside the larger pipe about 2" is the furnace exhaust connected through the larger ring #30 and screwed to the raised portion of ring #29. My furnace a vintage Hydro Flame Convection with dual direct vent, needed no power, and used a pilot light. Had the identical 2 pipe direct vent as yours. I built 2 rings similar to your drawing. Had 2 major issues: 1. Anytime the wind exceeded 20 mph, my pilot light would blow out even when the furnace side of my house was parked to the leeward side due to wind eddies.  2. At the exhaust cap which was about 1 3/4" from the side of the house would scorch the side surface above the cap and the moisture from burning Propane (1/2 pt. per 10#) would freeze on and below the exhaust when temp went -10 or below. Second year I re-designed using the Pipe Cap photo 1 from Menards for under $10. I cut off the bottom half at the black line and cut a hole on the outside flat surface for the exhaust pipe. This was my fresh air intake. Also filled the inside of the cap with a disassembled expanded metal filter from a motor home stove top exhaust filter.  Photo 1   Secured it to my house and ran the exhaust pipe through the hole in the end. Attached the exhaust pipe to a 2" x 3" aluminum gutter down spout used as a chimney. Photos 2 and 3. Totally solved my issues. You may also find a similar cap to photo 1 for the exhaust instead of the pipe. Most of the caps I was able to find had a 4" connection point so you would need to modify to 2" or whatever size you exhaust pipe is. How ever you do it, cover all openings with a screen to keep the Mud-daubers out as they love burned propane orifice area to build there nest.  Photo 2 & 3
    • sure looks like YHBB.  open fields and swamps close by? They like to hang out where the RWBB do.  Cannon SX30IS is pretty cheap online. 35 power zoom. good for still shots.   
    • Going to bait tomorrow with fryer grease, bread, dog food, cherry frosting, peanut butter, soft candies, raw white sugar, and popcorn. I am throwing everything at them tomorrow, hopefully the bears like the variety!
    • I don't know about that but I will certainly not write him off, if he can be a steady vet I will be happy. 
    • That's a great chicken recipe duff, but that steak n corn get my vote!! 
    • I was gonna say my yard has been thick with juvenile birds the last few days, always harder to ID birds this time of year. Had an albino something or other with a flock of birds, not sure I've seen an albino bird before. And just had a sharp shinned hawk hanging out on the branch above the feeders.  But I feed ALL of the birds......love them raptors. I will say the cowbirds around sure tolerate the dog or I getting pretty close to them.    
    • Had a decent trip.  We fished the evening of Aug. 9-Aug. 15.  Had 2 pretty good days, 2 bad days, and the rest were just so-so.  Dad, Uncle, and Grandpa don't like getting up early anymore so we usually outdrink the fish at night and sleep in mornings.   We have slowly been learning how to consistently catch fish on this lake.  The local guys don't provide any information and neither do the guys that have been making the trip for 20+ years.  Can't say I blame them much, but would have shortened the learning curve for us a little bit.  We found a bay a few years back that we can catch 10-16" walleye all day in, just a shallow weedy bay pulling spinners.  Usually get enough eyes' for dinner and then go search the reefs, shorelines, and islands for bigger fish.   I think we finally dialed in on some bottom bouncers and have 2-3 spots were we can go and most likely catch fish with the chance at some big ones.  1oz to 1-1/2oz BB with leeches or worms work the best on these spots.  2 spots are reefs topping out at 9-10fow and the other spot is a little flatter, with access to some shallow weeds.  We also deep troll suspended fish some evenings and don't catch a lot, but the ones we do are bigger fish.  We found iwe caught more fish when we were running and gunning.  Fish a spot for 20-30 minutes and then move on until we found some fish.  This kind of stinks for Grandpa but he understands we can't catch them if they are there and active. Biggest of the week was 26 1/4" walleye with 20-25 eyes' over 20".  I think I had 2 -25" and also a 37" pike the last evening.  Really fun time and scenery with the family.  Looking forward to next year and searching more of the lake.
    • Not a cowbird. We have several around here and they are generally dark-black grey and brown. The pictured bird almost looks as though it could be an immature yellow headed blackbird. Cowbirds are quite reclusive and we have been surprised they come out to our feeders, but they have become pretty regular customers. Like the deer that graze in the front yard. Last night we had the buck, doe and twin fawns and even though we talked softly to them they did not spook,  but seemed to simply acknowledge our presence on the deck and continued to feed. And of course, as usual, the black squirrels are gathering all MY walnuts!  darn.....I just can't win. The chipmunks eat my strawberries, deer eat tomato plants and squirrels eat my walnuts. I'm left with this old bottle of Beefeaters, a small bottle of vermouth and a few olives in a jar.  Things are tough out here in the wilderness.
  • Our Sponsors