      Fluid forum view allows members only to get right to the meat of this community; the topics. You can toggle between your preferred forum view just below to the left on the main forum entrance. You will see three icons. Try them out and see what you prefer.   Fluid view allows you, if you are a signed up member, to see the newest topic posts in either all forums (select none or all) or in just your favorite forums (select the ones you want to see when you come to Fishing Minnesota). It keeps and in real time with respect to Topic posts and lets YOU SELECT YOUR FAVORITE FORUMS. It can make things fun and easy. This is especially true for less experienced visitors raised on social media. If you, as a members want more specific topics, you can even select a single forum to view. Let us take a look at fluid view in action. We will then break it down and explain how it works in more detail.   The video shows the topic list and the forum filter box. As you can see, it is easy to change the topic list by changing the selected forums. This view replaces the traditional list of categories and forums.   Of course, members only can change the view to better suit your way of browsing.   You will notice a “grid” option. We have moved the grid forum theme setting into the main forum settings. This makes it an option for members only to choose. This screenshot also shows the removal of the forum breadcrumb in fluid view mode. Fluid view remembers your last forum selection so you don’t lose your place when you go back to the listing. The benefit of this feature is easy to see. It removes a potential barrier of entry for members only. It puts the spotlight on topics themselves, and not the hierarchical forum structure. You as a member will enjoy viewing many forums at once and switching between them without leaving the page. We hope that fluid view, the new functionality is an asset that you enjoy .
Sign in to follow this  
SimilarIsland

On board charger amps (pull)?

Recommended Posts

Does anyone know how many amps an MK345 (3 bank x 15 amps)Minnkota on board charger pulls on the 110v side? I'm trying to determine whether a Honda generator (5000 watts) will be enough to charge my batteries and another buddy's batteries on his boat. I couldn't find anything on the Minnkota HSOforum.

Thanks

SimilarIsland

Share this post


Link to post
Share on other sites

Your total watts would be 4950 if the charger would draw the max amount. The way to figure this out is PIE. Power= I current or amp x E voltage. 45 amps X 110 volts = 4950 watts.The problem would be if you and your buddy completely used up your batteries in one day the generator could only handle you for a while till you quit drawing max. amps.

Share this post


Link to post
Share on other sites

I'd say around 5 amps on the input side of the charger.

Using 120V as the standard voltage:

120VAC/12VDC = 10.

45A/10 = 4.5amps

You could use 14VDC too for "worst case" but it still isn't that much and the generator should handle it.

Share this post


Link to post
Share on other sites

You got it. Power is power, regardless if it's AC or DC. You may have to add in a little extra for the losses due to the transformer, etc, but your calculation is definitely in the ballpark.

We had an interesting thing happen the other day at work with a Honda generator and battery charger/inverter that may be related to this. On a piece of equipment we use a charger/inverter. What this does is takes 120VAC line power and charges a 12V battery. If the line power is removed (power outage), the charger turns into an inverter and pulls off of the battery that it had previously be charging, transforms it to 120VAC, and then powers the equipment to keep it running until line power is restored. We had to drop the line power so we connected the generator but the charger/inverter wouldn't change back to "charge mode" like it should after a three second delay. I didn't get a chance to look into it further but we are suspecting that the generator is putting out a square wave rather than a clean sine wave and the charger/inverter doesn't like it, so it stays on "inverter mode". Just a theory right now, but you may want to test your configuration to make sure the charger will function as you want it to.

Share this post


Link to post
Share on other sites

Great! Thanks.

One of my friends was also telling me to watch out when the generator runs out of gas. He thinks that's what blew his charger on the last trip.

Share this post


Link to post
Share on other sites

You got it. Power is power, regardless if it's AC or DC. You may have to add in a little extra for the losses due to the transformer, etc, but your calculation is definitely in the ballpark.

We had an interesting thing happen the other day at work with a Honda generator and battery charger/inverter that may be related to this. On a piece of equipment we use a charger/inverter. What this does is takes 120VAC line power and charges a 12V battery. If the line power is removed (power outage), the charger turns into an inverter and pulls off of the battery that it had previously be charging, transforms it to 120VAC, and then powers the equipment to keep it running until line power is restored. We had to drop the line power so we connected the generator but the charger/inverter wouldn't change back to "charge mode" like it should after a three second delay. I didn't get a chance to look into it further but we are suspecting that the generator is putting out a square wave rather than a clean sine wave and the charger/inverter doesn't like it, so it stays on "inverter mode". Just a theory right now, but you may want to test your configuration to make sure the charger will function as you want it to.

Depends on the Honda generator series. The ones with inverter technology should be as clean, or maybe even cleaner, than the AC power off the grid.

The non-inverter models may not be perfect sine wave, but unlikely to be square waves. Honda HSOforum has some pictures/representations of the waveforms from its various generator series.

Share this post


Link to post
Share on other sites

After posting I looked up the Honda generators and they are a square wave unless it's one of the generators in their "Inverter" series, which the generator in question is not. This would make sense as to why the charger/inverter didn't work.

It isn't a square wave in the classic sense, but it has stepped characteristics instead of a smooth sine curve. This chops off the peak and that is were the issues will happen as many sensitive devices depend on that peak to operate. I suppose it could be referred to as a modified square wave or maybe it's even a psuedo sine wave.

Share this post


Link to post
Share on other sites

On Rainy Lake we had a 1000 watt Honda generator. 2 boats had 2 bank chargers 20 amp total. 1 boat had a 3 bank charger that was 25 total amps. The 4th boat had a 1 bank 6 amp charger. We could plug a combination of any 3 boats in on most nights. It couldn't handle all 4 at once.

After one very windy day we could only plug in 2 boats if the 3 bank was one of them.

We ran the generator out of gas every night and had no problems with the chargers or batteries.

The 5000 watt generator should charge your 2 boats with a combined 90 amps easily.

Share this post


Link to post
Share on other sites

On Rainy Lake we had a 1000 watt Honda generator. 2 boats had 2 bank chargers 20 amp total. 1 boat had a 3 bank charger that was 25 total amps. The 4th boat had a 1 bank 6 amp charger. We could plug a combination of any 3 boats in on most nights. It couldn't handle all 4 at once.

After one very windy day we could only plug in 2 boats if the 3 bank was one of them.

We ran the generator out of gas every night and had no problems with the chargers or batteries.

The 5000 watt generator should charge your 2 boats with a combined 90 amps easily.

The chargers work on 120V, the 1000W generator is about 8.5 Amps at 120 volts.

Two 20 Amp (at 12v) chargers would be roughly 5 Amps @ 120V, probably closer to 6 when you count losses. Adding the additional 25 A (at 12 v) of the three bank charger would bring the 120 V load to 6.5 Amps theoretical, but likely closer to 8 or 9 Amps at 120 V considering losses. So, the math works out near perfectly with what you observed.

About the 5,000 watt generator, assume it will be about 4000w continuous. This means that it would support roughly 300 Amps of charging at 12 V.

4000W divide by 12 V = 333 Amps. Reduce that to account for conversion losses and you end up with being able to support about 300 Amps of battery charging current.

Share this post


Link to post
Share on other sites

I just got a power converter for my fish house and a 1000w generator- will da generator run the converter???

What do you mean by power converter, 120V to 12V?

Watts are universal meaning that 1000W at 120V is equivalent to 1000W at 12V. So, your 1000W generator would support a converter capable of putting out 1000W at 12V (~80 Amps) from the 1000W at 120V (~8 Amps).

There is some loss in the 120V to 12V converson so it won't come out exactly like that, but you get the idea how it works in general.

Share this post


Link to post
Share on other sites
Guest
This topic is now closed to further replies.
Sign in to follow this  



  • Posts

    • We had a tire blow out a few weeks ago while heading to Zumbro Falls so I just put 4 new tires on the camper last week. Decided to go with the new Goodyear Endurance tires. I also packed all the bearings while I had the wheels off.  
    • Has anyone tried using a picnic basket? 
    • Last nites work. 13 qts stewed tomatoes, 5 pints juice and 15 pints salsa!
    • I'll second that!! Gotta get some more cob cawn today myself....
    • From the  picture it is a male yellow headed blackbird; IMO there is even a faint white bar on the wings which may be what you describe as "the ring on its back" and the black smudge under and behind the eye.  I can't tell about the bill, but on a cowbird the bill is quite heavy;  not nearly so stout on the YH blackbird. Immature male yellow headed black birds are not so bright yellow as the adults, and there should definitely be some young of the year fledged by this time of the year.   If the picture is not accurate then we will need a better photo to do better than that.  IMO This picture does not show a brown headed cowbird.  Most cell phones will take a better picture and if it is tame enough please post another or even better a couple more.  The more different poses the better. Yellow headed blackbirds are almost invariably connected to swampy areas, especially those with cattail fringes.  They also tend to be around in groups, especially groups nesting in the same swamp not mixed in with red winged black birds.   The females of both species are quite drab, and quite distinct from those of the cowbirds.
    • I do live by a river and have lots of RWBB, maybe it will yellow up. That's a very distinct rusty brown ring on it's back though, I didn't see that in any of the YHBB pictures.
    • This furnace has 2 pipes. The larger pipe about 4" is the air intake is supported through ring #29. The smaller pipe inside the larger pipe about 2" is the furnace exhaust connected through the larger ring #30 and screwed to the raised portion of ring #29. My furnace a vintage Hydro Flame Convection with dual direct vent, needed no power, and used a pilot light. Had the identical 2 pipe direct vent as yours. I built 2 rings similar to your drawing. Had 2 major issues: 1. Anytime the wind exceeded 20 mph, my pilot light would blow out even when the furnace side of my house was parked to the leeward side due to wind eddies.  2. At the exhaust cap which was about 1 3/4" from the side of the house would scorch the side surface above the cap and the moisture from burning Propane (1/2 pt. per 10#) would freeze on and below the exhaust when temp went -10 or below. Second year I re-designed using the Pipe Cap photo 1 from Menards for under $10. I cut off the bottom half at the black line and cut a hole on the outside flat surface for the exhaust pipe. This was my fresh air intake. Also filled the inside of the cap with a disassembled expanded metal filter from a motor home stove top exhaust filter.  Photo 1   Secured it to my house and ran the exhaust pipe through the hole in the end. Attached the exhaust pipe to a 2" x 3" aluminum gutter down spout used as a chimney. Photos 2 and 3. Totally solved my issues. You may also find a similar cap to photo 1 for the exhaust instead of the pipe. Most of the caps I was able to find had a 4" connection point so you would need to modify to 2" or whatever size you exhaust pipe is. How ever you do it, cover all openings with a screen to keep the Mud-daubers out as they love burned propane orifice area to build there nest.  Photo 2 & 3
    • sure looks like YHBB.  open fields and swamps close by? They like to hang out where the RWBB do.  Cannon SX30IS is pretty cheap online. 35 power zoom. good for still shots.   
    • Going to bait tomorrow with fryer grease, bread, dog food, cherry frosting, peanut butter, soft candies, raw white sugar, and popcorn. I am throwing everything at them tomorrow, hopefully the bears like the variety!
  • Our Sponsors