      Fluid forum view allows members only to get right to the meat of this community; the topics. You can toggle between your preferred forum view just below to the left on the main forum entrance. You will see three icons. Try them out and see what you prefer.   Fluid view allows you, if you are a signed up member, to see the newest topic posts in either all forums (select none or all) or in just your favorite forums (select the ones you want to see when you come to Fishing Minnesota). It keeps and in real time with respect to Topic posts and lets YOU SELECT YOUR FAVORITE FORUMS. It can make things fun and easy. This is especially true for less experienced visitors raised on social media. If you, as a members want more specific topics, you can even select a single forum to view. Let us take a look at fluid view in action. We will then break it down and explain how it works in more detail.   The video shows the topic list and the forum filter box. As you can see, it is easy to change the topic list by changing the selected forums. This view replaces the traditional list of categories and forums.   Of course, members only can change the view to better suit your way of browsing.   You will notice a “grid” option. We have moved the grid forum theme setting into the main forum settings. This makes it an option for members only to choose. This screenshot also shows the removal of the forum breadcrumb in fluid view mode. Fluid view remembers your last forum selection so you don’t lose your place when you go back to the listing. The benefit of this feature is easy to see. It removes a potential barrier of entry for members only. It puts the spotlight on topics themselves, and not the hierarchical forum structure. You as a member will enjoy viewing many forums at once and switching between them without leaving the page. We hope that fluid view, the new functionality is an asset that you enjoy .
  • RECEIVE THE GIFTS MEMBERS SHARE WITH YOU HERE...THEN...CREATE SOMETHING TO ENCHANT OTHERS THAT YOU WANT TO SHARE

    You know what we all love...

    When you enchant people, you fill them with delight and yourself in return. Have Fun!!!

Sign in to follow this  
Swill

Running power to a shed or garage

Recommended Posts

Hello gang-

I recently build an exterior shed (14 x 22); which is about 75 yards from the house. I am now thinking an outside overhead light, a few interior lights and 2-3 outlets would be nice to have in there. Any suggestions as to how I can run power?

Also, how can I determine how much power I will be pulling? I have a large compressor and would like to use the shed to charge batteries, power tools, and occasionally run the miter saw.

Lastly, if I want to connect in one of those low volt exterior landscape lighting systems; do I need to plan for that now, or are they pretty easy to add later.

Thanks

Swill

Share this post


Link to post
Share on other sites

Best to get a sparky to answer your questions.With all the things you want to run sounds like you need 2 underground rated leads each off its own breaker GFI protected 15 A. Buried at least 18 inches. While your diggin you could be waiting for a sparkies reply.

Share this post


Link to post
Share on other sites

Use UF feeder cable, or better yet, pvc pipe, a few 20 amp circuits should be suffice. Make sure all recepticals are GFCI. As for the landscape lighting, the only two things you should preplan for is going under concrete, asphalt, driveways etc., and where you plan to feed it from, the 120 volt source. most low voltage lighting wiring is run in the mulch/rocks etc.

Good Luck

Share this post


Link to post
Share on other sites

Why all GFCI's? I find them bothersome when pulling heavy loads like a compressor. Maybe they were just cheap ones though.

It is nice to be able to reset right there instead of running in the house or garage.

You would recommend 12 wire, right?

Share this post


Link to post
Share on other sites

depending on the length to the garage for the wire size, you need less than 5 percent voltage drop from the service to the farthest outlet. In the case listed above, I would definatly use 10's, probably 8's. As for the GFCI'S the nec requires them. If you have a problem tripping it could be an issue with the equipment.

Voltage drop= 2*12.9*current*length (in ft)/circular mils of wire

2 * 12.9 * 20 * 225/10380= 11.18 volts for #10 wire

2 * 12.9 * 20 * 225/16510= 7.03 volts for #8 wire

I would use # 8's to get me to the garage, then 12's from there on.

If someone could check my math/formula's, that would be great, haven't used them in a while.

Share this post


Link to post
Share on other sites

If you GFCI protect the UF wire you will only have to burry it 12". You can run conduit and not GFCI protect it but that will have to be 18".

You have to use GFCIs in there because the NEC (210.8) states "All 125 volt, single phase, 15 and 20 amp receptacles installed in the locations specified in (1) thru (8) shall have ground-fault circuit-interupter protection for personnel.

(2) Garages, and also accessory building that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use.

Do you have a sub panel in the garage or are you going to come out of the house panel? How many empty breaker spots do you have? Is it a 100 or 200 amp panel? Before I tell you how I would do it, what is the load on your air compressor? How many and what type of lights do you want? Are you just going to charge some batteries or are you going to fire up 10 electric smokers in there? Heat? Put a list together of what you are going to run in there and how many are going to run at the same time and I can give you a rough load calc.

If your just going to run a light or two with one receptacle I'd just run UF cable fed off of a GFCI in the garage, but if you plan on more than that it can get a little more involved. Depending on the size of your air compressor you might need to go bigger than 12ga wire.

Share this post


Link to post
Share on other sites

Sparky, depending on what voltage drop formula you use, if you have a full 20 amp load at start up you will need to run 8s.

Share this post


Link to post
Share on other sites

Wow, good info.

I didn't know that garages had to be all GFCI's. Thanks.

Swill, has some work cut out for him. \:\)

Share this post


Link to post
Share on other sites

If you can answer a few of those questions it will make it alot easier to give you a good way of doing it. Its always better to leave yourself some room for future usage it will be much easier to add on to in the future if you've already got everything there.

Share this post


Link to post
Share on other sites

And yet a homeowner can wire their own new house. Never understood that one. Yet they have to hire a licensed plumber?????????

Personally I think everything should be professionally done. It would make our homes that much better.

Share this post


Link to post
Share on other sites

 Originally Posted By: Roofer

Personally I think everything should be professionally done. It would make our homes that much better.

This might be a good statement for the "Rich & Lazy" section of this forum grin.gif. But most Outdoorsmen are also the do-it-yourselfers type of people. Although hiring it done gives you more time to fish. All in all this is a pretty easy job once you have the codes figured out and what materials you need.

Share this post


Link to post
Share on other sites

You got it D2E,But not being a sparkie I cant give info here but I do do my own.Puttin power in soon nextdoor on other lot.

Where ya been I just emailed you 1/2 hr. ago.

Share this post


Link to post
Share on other sites

I would run at least 60 amps (100 is better)out to that shed with a sub panel out there.

When I built a new detached garage we added an extra 100 amp Tri-Plex wire directly from the meter 18" underground into the garage where I installed a 100 amp Panel. I then ran another 100 amp wire to my other shed and put a sub panel in there. Now I have all the power I could ever want (welder etc.) in both the garage and shed.

So I have 2 100 amp wires coming out of the meter, one for the house and one for the garage and shed. If you get a Pro to run the underground wire and connect to the panel, the rest is pretty straight forward.

Share this post


Link to post
Share on other sites

100 amps to a shed. What are you going to be doing in that shed grin.gif?

I ran a 50 sub panel out to my garage and run welders, plasma cutter, compressors, lights, stereo and other junk. It worked out just fine.

I think a 30amp should be more than fine for a shed. IMO, above this, you are just spending money you do not have to. Most homes are run off of a 100amp.

Share this post


Link to post
Share on other sites

I agree with shack, that power is not needed, but still wouldn't hurt if you can get a panel for say.....free!

If the shed has it's own panel, is it still needed to have the GFCI's?

Still confuses me. I haven't read that anywhere except here. Are you sure that is a residential code?

Share this post


Link to post
Share on other sites

 Originally Posted By: shackbash
100 amps to a shed. What are you going to be doing in that shed grin.gif?

I ran a 50 sub panel out to my garage and run welders, plasma cutter, compressors, lights, stereo and other junk. It worked out just fine.

I think a 30amp should be more than fine for a shed. IMO, above this, you are just spending money you do not have to. Most homes are run off of a 100amp.

My whole garage is on 30 amp its fine,cant run the table saw,joiner,planer at the same time any way without help and when I have help we never overloaded.

Share this post


Link to post
Share on other sites

The electrical inspector (in my area) told me that in the shed the first outlet on each circuit needed to be GFCI, but others beyond that on the same circuit didn't need to be.

Tri-Plex wire was still pretty cheap back when I did my stuff, so having the extra power available if needed is nice. The only extra money is for the bigger wire.

Share this post


Link to post
Share on other sites

Plus the price diff. from a 30amp switch to a 100amp.

Might as well if you can do it. It all adds up to future stuff and good sale points if you ever sell. It does all add up in the end.

Share this post


Link to post
Share on other sites

Inspector is correct, because all other receptacles would then

be downstream from the gfci on the "load side". If adding new

panel remember to undo bonding jumper in sub-panel then put in new ground rod. Or make sure you pull a new ground.

Share this post


Link to post
Share on other sites

 Originally Posted By: Roofer
Are you sure that is a residential code?

There is only one NEC. There isn't a commercial book and a residential book. It all falls into that 750 pages. The knowledge of the book falls into where to find it and how to apply it to the proper application.

Share this post


Link to post
Share on other sites

 Originally Posted By: Roofer
And yet a homeowner can wire their own new house. Never understood that one. Yet they have to hire a licensed plumber?????????

I'm pretty sure a homeowner can do his own plumbing too. Can anyone confirm or deny this?

Share this post


Link to post
Share on other sites

Just an FYI, I am more than what my username implies.........

Share this post


Link to post
Share on other sites

I have always been told also that GFCI's are at the beginning of a run only. Not saying that is correct, but that is why I asked.

Share this post


Link to post
Share on other sites

I went back and edited it. It wasn't aimed at you or anyone in particular.

You can put a GFCI at the begining and protect the other receptacles downstream from it (the cheap route) or put a GFCI in every hole (the good looking route). Both accomplish the same thing. If you are going to run more than one GFCI on the same circuit you DO NOT feed the second one from the protected side of the first one. Now if you have regular receptacles between them it gets tricky....

Share this post


Link to post
Share on other sites
Guest
This topic is now closed to further replies.
Sign in to follow this  



  • Your Responses - Share & Have Fun :)

    • Doesn't get any better than that. Pic says it all. Congrats  
    • Well not the most attractive option but when the kids are out playing in the sprinkler you could get a roll of nonslip pool matting to roll out then put in the garage during the fall-winter? 
    •   OK, then how about stripping the sealer if that is what makes it slippery.   After a few years it really isn't necessary, since the concrete is mostly cured by then (yeah it keeps curing for decades but most of it is done in a year or two).     I guess if you like the glossy look then maybe the sand in the sealer thing is worth a try.
    • Season ended just like I thought it would and happy Leipold held true to his word and moved on from Fletcher...he did some good things but overall did a poor job building a team that can compete at a high level unfortunately.  It will be interesting to see how the new GM handles this situation...getting rid of under-performers will not be easy and what in return? Going to be one of those down before heading back up deals. Coyle will be the first to go IMO, Granny can go as far as I'm concerned...gotta sign Zucker even though he was terrible in the playoffs, Nino is a question mark, Staal might need to go with the up year he had but long in the tooth and now would be the only time to get anything for him, Ennis (terrible player) will be bought out, Foligno (terrible) probably not tradeable with his contract...enjoy the ride Wild fans!
    • We packed four of us in the blind and had a blast!  Just about ready to give up and gave "one last call" only to have the birds blow up not 30 yards away from us.  One of the gobblers rubbed against the blind for two feet as he walked into the deeks- pretty dang cool!  Ryan made a perfect shot and dropped the bird in his tracks.  
    • Ryan.pdf The pdf shows up as a link for me.  Is that ok Borch?  
    • Twins are 33-91 against the Yankees since 2002! Its unbelievable how awful they play against them.    Stanton absolutely murdered that hanging curveball for a HR last night.
    • I was looking for reviews last night but only found a handful and they didn't really give me that much info. They seemed to be overall positive reviews but all were written after recently applying it so no info on longevity. 
    • Stamped concrete looks great, but not very functional and it requires maintenance too, like every couple of years or so.   ....and how do you get the non-peeled, non-flaked area cleaned?