      Fluid forum view allows members only to get right to the meat of this community; the topics. You can toggle between your preferred forum view just below to the left on the main forum entrance. You will see three icons. Try them out and see what you prefer.   Fluid view allows you, if you are a signed up member, to see the newest topic posts in either all forums (select none or all) or in just your favorite forums (select the ones you want to see when you come to Fishing Minnesota). It keeps and in real time with respect to Topic posts and lets YOU SELECT YOUR FAVORITE FORUMS. It can make things fun and easy. This is especially true for less experienced visitors raised on social media. If you, as a members want more specific topics, you can even select a single forum to view. Let us take a look at fluid view in action. We will then break it down and explain how it works in more detail.   The video shows the topic list and the forum filter box. As you can see, it is easy to change the topic list by changing the selected forums. This view replaces the traditional list of categories and forums.   Of course, members only can change the view to better suit your way of browsing.   You will notice a “grid” option. We have moved the grid forum theme setting into the main forum settings. This makes it an option for members only to choose. This screenshot also shows the removal of the forum breadcrumb in fluid view mode. Fluid view remembers your last forum selection so you don’t lose your place when you go back to the listing. The benefit of this feature is easy to see. It removes a potential barrier of entry for members only. It puts the spotlight on topics themselves, and not the hierarchical forum structure. You as a member will enjoy viewing many forums at once and switching between them without leaving the page. We hope that fluid view, the new functionality is an asset that you enjoy .
Sign in to follow this  
Swill

Running power to a shed or garage

Recommended Posts

Hello gang-

I recently build an exterior shed (14 x 22); which is about 75 yards from the house. I am now thinking an outside overhead light, a few interior lights and 2-3 outlets would be nice to have in there. Any suggestions as to how I can run power?

Also, how can I determine how much power I will be pulling? I have a large compressor and would like to use the shed to charge batteries, power tools, and occasionally run the miter saw.

Lastly, if I want to connect in one of those low volt exterior landscape lighting systems; do I need to plan for that now, or are they pretty easy to add later.

Thanks

Swill

Share this post


Link to post
Share on other sites

Best to get a sparky to answer your questions.With all the things you want to run sounds like you need 2 underground rated leads each off its own breaker GFI protected 15 A. Buried at least 18 inches. While your diggin you could be waiting for a sparkies reply.

Share this post


Link to post
Share on other sites

Use UF feeder cable, or better yet, pvc pipe, a few 20 amp circuits should be suffice. Make sure all recepticals are GFCI. As for the landscape lighting, the only two things you should preplan for is going under concrete, asphalt, driveways etc., and where you plan to feed it from, the 120 volt source. most low voltage lighting wiring is run in the mulch/rocks etc.

Good Luck

Share this post


Link to post
Share on other sites

Why all GFCI's? I find them bothersome when pulling heavy loads like a compressor. Maybe they were just cheap ones though.

It is nice to be able to reset right there instead of running in the house or garage.

You would recommend 12 wire, right?

Share this post


Link to post
Share on other sites

depending on the length to the garage for the wire size, you need less than 5 percent voltage drop from the service to the farthest outlet. In the case listed above, I would definatly use 10's, probably 8's. As for the GFCI'S the nec requires them. If you have a problem tripping it could be an issue with the equipment.

Voltage drop= 2*12.9*current*length (in ft)/circular mils of wire

2 * 12.9 * 20 * 225/10380= 11.18 volts for #10 wire

2 * 12.9 * 20 * 225/16510= 7.03 volts for #8 wire

I would use # 8's to get me to the garage, then 12's from there on.

If someone could check my math/formula's, that would be great, haven't used them in a while.

Share this post


Link to post
Share on other sites

If you GFCI protect the UF wire you will only have to burry it 12". You can run conduit and not GFCI protect it but that will have to be 18".

You have to use GFCIs in there because the NEC (210.8) states "All 125 volt, single phase, 15 and 20 amp receptacles installed in the locations specified in (1) thru (8) shall have ground-fault circuit-interupter protection for personnel.

(2) Garages, and also accessory building that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use.

Do you have a sub panel in the garage or are you going to come out of the house panel? How many empty breaker spots do you have? Is it a 100 or 200 amp panel? Before I tell you how I would do it, what is the load on your air compressor? How many and what type of lights do you want? Are you just going to charge some batteries or are you going to fire up 10 electric smokers in there? Heat? Put a list together of what you are going to run in there and how many are going to run at the same time and I can give you a rough load calc.

If your just going to run a light or two with one receptacle I'd just run UF cable fed off of a GFCI in the garage, but if you plan on more than that it can get a little more involved. Depending on the size of your air compressor you might need to go bigger than 12ga wire.

Share this post


Link to post
Share on other sites

Wow, good info.

I didn't know that garages had to be all GFCI's. Thanks.

Swill, has some work cut out for him. \:\)

Share this post


Link to post
Share on other sites

If you can answer a few of those questions it will make it alot easier to give you a good way of doing it. Its always better to leave yourself some room for future usage it will be much easier to add on to in the future if you've already got everything there.

Share this post


Link to post
Share on other sites

And yet a homeowner can wire their own new house. Never understood that one. Yet they have to hire a licensed plumber?????????

Personally I think everything should be professionally done. It would make our homes that much better.

Share this post


Link to post
Share on other sites

 Originally Posted By: Roofer

Personally I think everything should be professionally done. It would make our homes that much better.

This might be a good statement for the "Rich & Lazy" section of this forum grin.gif. But most Outdoorsmen are also the do-it-yourselfers type of people. Although hiring it done gives you more time to fish. All in all this is a pretty easy job once you have the codes figured out and what materials you need.

Share this post


Link to post
Share on other sites

You got it D2E,But not being a sparkie I cant give info here but I do do my own.Puttin power in soon nextdoor on other lot.

Where ya been I just emailed you 1/2 hr. ago.

Share this post


Link to post
Share on other sites

I would run at least 60 amps (100 is better)out to that shed with a sub panel out there.

When I built a new detached garage we added an extra 100 amp Tri-Plex wire directly from the meter 18" underground into the garage where I installed a 100 amp Panel. I then ran another 100 amp wire to my other shed and put a sub panel in there. Now I have all the power I could ever want (welder etc.) in both the garage and shed.

So I have 2 100 amp wires coming out of the meter, one for the house and one for the garage and shed. If you get a Pro to run the underground wire and connect to the panel, the rest is pretty straight forward.

Share this post


Link to post
Share on other sites

100 amps to a shed. What are you going to be doing in that shed grin.gif?

I ran a 50 sub panel out to my garage and run welders, plasma cutter, compressors, lights, stereo and other junk. It worked out just fine.

I think a 30amp should be more than fine for a shed. IMO, above this, you are just spending money you do not have to. Most homes are run off of a 100amp.

Share this post


Link to post
Share on other sites

I agree with shack, that power is not needed, but still wouldn't hurt if you can get a panel for say.....free!

If the shed has it's own panel, is it still needed to have the GFCI's?

Still confuses me. I haven't read that anywhere except here. Are you sure that is a residential code?

Share this post


Link to post
Share on other sites

 Originally Posted By: shackbash
100 amps to a shed. What are you going to be doing in that shed grin.gif?

I ran a 50 sub panel out to my garage and run welders, plasma cutter, compressors, lights, stereo and other junk. It worked out just fine.

I think a 30amp should be more than fine for a shed. IMO, above this, you are just spending money you do not have to. Most homes are run off of a 100amp.

My whole garage is on 30 amp its fine,cant run the table saw,joiner,planer at the same time any way without help and when I have help we never overloaded.

Share this post


Link to post
Share on other sites

The electrical inspector (in my area) told me that in the shed the first outlet on each circuit needed to be GFCI, but others beyond that on the same circuit didn't need to be.

Tri-Plex wire was still pretty cheap back when I did my stuff, so having the extra power available if needed is nice. The only extra money is for the bigger wire.

Share this post


Link to post
Share on other sites

Plus the price diff. from a 30amp switch to a 100amp.

Might as well if you can do it. It all adds up to future stuff and good sale points if you ever sell. It does all add up in the end.

Share this post


Link to post
Share on other sites

Inspector is correct, because all other receptacles would then

be downstream from the gfci on the "load side". If adding new

panel remember to undo bonding jumper in sub-panel then put in new ground rod. Or make sure you pull a new ground.

Share this post


Link to post
Share on other sites

 Originally Posted By: Roofer
Are you sure that is a residential code?

There is only one NEC. There isn't a commercial book and a residential book. It all falls into that 750 pages. The knowledge of the book falls into where to find it and how to apply it to the proper application.

Share this post


Link to post
Share on other sites

 Originally Posted By: Roofer
And yet a homeowner can wire their own new house. Never understood that one. Yet they have to hire a licensed plumber?????????

I'm pretty sure a homeowner can do his own plumbing too. Can anyone confirm or deny this?

Share this post


Link to post
Share on other sites

I have always been told also that GFCI's are at the beginning of a run only. Not saying that is correct, but that is why I asked.

Share this post


Link to post
Share on other sites

I went back and edited it. It wasn't aimed at you or anyone in particular.

You can put a GFCI at the begining and protect the other receptacles downstream from it (the cheap route) or put a GFCI in every hole (the good looking route). Both accomplish the same thing. If you are going to run more than one GFCI on the same circuit you DO NOT feed the second one from the protected side of the first one. Now if you have regular receptacles between them it gets tricky....

Share this post


Link to post
Share on other sites
Guest
This topic is now closed to further replies.
Sign in to follow this  



  • Posts

    • Free agency is far from a sure thing, if there are young centers out there (big if) you have to compete with maybe 10 or 20 other teams and pay way over what you should. You have control of nothing and are at the whims of a player everyone is chasing. Same with trades, very easy to swing and miss. By most account we were in on Ryan Johansen with the Preds but Columbus wanted Jones over Brodin and I don't blame them. 
    • Good stuff but time wiill tell. Not buying the "oh we might lose him as a UFA"...so what, with that kind of money we could buy just as good and younger to give us more of a future...which we desparately need to be thinking about.  Fletch is walking a tightrope and it is going to break IMO.
    • Come on BB, you are better than that. You as much as anyone know that ONE player doesn't make an NHL Team a Stanley Cup contender so why put that blame on him. Sure, a player like Crosby certainly helps, but we aren't talking about the money that Crosby is getting here either. Comparing Koivu's contracts to equivalent players with similar production is quite compelling. He has performed better than many of his peers for his current contract and with the lower AV of his new deal if he continues similar numbers it will be a bargain. I wasn't too happy about the NMC either, but I take that as a bargaining chip so CF didn't have to go with a longer term deal. 2 years is sufficient and I think it works well for both parties. You are right, there are many people out there with more knowledge about the market and what he could have gotten elsewhere and when it may have made sense to sign him, but the fact is you don't want to wait to sign him until after the season for if no other reason at all than to allow him to be a UFA and hear other offers. This will be my last post about the Koivu extension because clearly we don't see eye to eye on whether it made/makes sense, but I assure you there are a large number of "hockey minds" that are in agreement with me on this. Here is some afternoon reading for you: https://www.hockeywilderness.com/2017/9/20/16332552/mikko-koivu-contract-extension-minnesota-wild-criticism-overpaid-chuck-fletcher-cap-space
    • Red admiral i believe.
    • Btw......for you bass purists .... a couple days before the above success, I located mostly largemouth with one smallmouth on the edge of bulrushes adjacent to a deep drop off.  Probably a dozen fish in 20 casts with a Senko. Nothing of any real size. Always fun getting fish on four or five consecutive casts.
    • Great find! I did a little research and did not find an I.D.  Hopefully someone will know what it is.
    • You are 100% correct... a guy has to be smart about it. There is nothing magic about inverters... its takes a lot of DC juice to make a little AC juice. On the flipside though, I have a 120vac 32" TV/DVD player that only draws 51 watts AC.... meaning that it should (hypothetically) only draw 4.25 amps DC. Even with a 15% draw added for the inefficiency of the inverter, I am still under 5 amp. Usually I will run the generator for a few hours between 10 am and 2 pm. Then it is off until 7 pm or so... Then I will fill it up and let it run through out the night. It will run about 9 hrs on eco, so by 4 am or so it is out of gas... but the batteries are topped off nice to run the routine again. The 4 hr run isn't necessary, but does offer some security. With a 5 and a 7 yr old fishing with me the majority of the time, the TV usually doesn't turn off during the day.
    • I believe the crawlers are not natural forage and using them as bait emulates large larvae.  
    • Like I stated earlier and others with more knowledge than anyone on here have as well..we should have waited...I also was unaware of the no trade clause which he was able to get without any less $$...pure stupidity...we'll know in 8/9 months how this pans out...it boot straps us from further improving the team with younger talent is my main issue. As far as a captain, lifelong wild...blah blah blah....if he is such a pillar, such a great player, such a leader of the team...where has he taken us? The playoff record speaks for itself....time to dump guys like Koivu at the soonest opportunity who have done all they can or at least decrease their pay in later years not increase them...they took us as far as they could...and we've already got vets like Parise, Suter, Spurgeon, Granlund, Coyle, Brodin locked in on long term deals; give one of them the C to carry us forward.  
  • Our Sponsors