      Fluid forum view allows members only to get right to the meat of this community; the topics. You can toggle between your preferred forum view just below to the left on the main forum entrance. You will see three icons. Try them out and see what you prefer.   Fluid view allows you, if you are a signed up member, to see the newest topic posts in either all forums (select none or all) or in just your favorite forums (select the ones you want to see when you come to Fishing Minnesota). It keeps and in real time with respect to Topic posts and lets YOU SELECT YOUR FAVORITE FORUMS. It can make things fun and easy. This is especially true for less experienced visitors raised on social media. If you, as a members want more specific topics, you can even select a single forum to view. Let us take a look at fluid view in action. We will then break it down and explain how it works in more detail.   The video shows the topic list and the forum filter box. As you can see, it is easy to change the topic list by changing the selected forums. This view replaces the traditional list of categories and forums.   Of course, members only can change the view to better suit your way of browsing.   You will notice a “grid” option. We have moved the grid forum theme setting into the main forum settings. This makes it an option for members only to choose. This screenshot also shows the removal of the forum breadcrumb in fluid view mode. Fluid view remembers your last forum selection so you don’t lose your place when you go back to the listing. The benefit of this feature is easy to see. It removes a potential barrier of entry for members only. It puts the spotlight on topics themselves, and not the hierarchical forum structure. You as a member will enjoy viewing many forums at once and switching between them without leaving the page. We hope that fluid view, the new functionality is an asset that you enjoy .
1lessdog

Empire furance

Recommended Posts

I bought a Empire direct vent furnace off hsolist for $100. Its the 15000 BTU md. I check to make sure it worked before I cut a 5" hole in the wall and it did. My question is looking thru the sight glass how high should the flame be above the burners. I have it hooked to a 20 lb cyl with a low pressure reg. And the flames are maybe 3/16 above the burner all the way around. Should I take the reg off?

IMG_4853 (1).jpg

20161129_115228.jpeg

Edited by 1lessdog

Share this post


Link to post
Share on other sites

My recommendation is Do Not remove the regulator. The 20# tank produces 100 + # of pressure at the regulator. The regulator is a low presser regulator pre-set at 6 ounces of pressure to your furnace/stove which is what you need to run your LP furnace, stove etc.

 

The burner on the stove in your picture produces 9,000 BTU's set on Hi. and most likely has a flame about 1 inch or so in height. You may have one of 2 issues. The pipe from the regulator should be 3/8" id. If you used 1/4" copper tubing, there may not be enough volume of LP getting to the furnace. 1/2" tubing is also good. Second might be a plugged orifice. That's the small copper part connected to our furnace gas line just below the larger tubes with large holes in it called the venture. The diameter of the hole in the orifice should be .0469 inches. Same as a 3/64 drill bit to produce 15,000 BTU. You can clean the orifice using one of the cleaning wires from a Meg welding supply shop which requires disassembly of your furnace. If the stove burner has a 1" or so high flame, problem is not the tubing size if you connected to the same line.

 

This photo is from my wheel house furnace has a 5.5" dia. burner and is running at 12,300 BTU to get an idea of how high the flame should be. Your burner may be in-line but should have a similar flame.

Furnace fire upgrade (900x506).jpg

Share this post


Link to post
Share on other sites

I was thinking about hooking up a air line and try blow out anything what maybe blocking the gas flow. I used a  rubber hose from mister heater that was 12ft long and 3/8 dia.

 

Is there anyone in the Moorhead area that could take a look at it?

Edited by 1lessdog

Share this post


Link to post
Share on other sites

Im running off two different tanks. I will go to one tank when I have everything running smooth. The burners on the stove top have a flame of a inch or maybe a little more. So the stove top is good. I just get to much moisture in the house is why I put in the Empire furnace.

Share this post


Link to post
Share on other sites

DO NOT RUN IT WITH THE REGULATOR OFF.  Being used it could have a corroded gas inlet but I would try a different regulator first. I'm thinking they have a high and low flame don't they Sea Hage?

Edited by Hawg

Share this post


Link to post
Share on other sites

Mine is either Pilot or On. If you have a gas pressure gauge you can check the pressure coming out of the control , there is a small screw at the test port, the screw won't come out but all you do is loosen it a couple turns and hold the tester hose over it. I think it should be 11 inches of water. My flame is only 1/4" high at best.

Edited by Sea Hage

Share this post


Link to post
Share on other sites

I also have a DV-215 and I kind of thought I was also having a problem with the 3-5" secondary flame height called out in the install manual.  Looking through the vision window, I couldn't see it.  I only saw the height that you were seeing, which was really the primary flame height, not the secondary height.  I worked through all sorts of things on my end trying to make sure everything was up to spec.  I replaced the regulator at the tank.  I took all sorts of stuff apart and cleaned it.  Checked my rubber hose for proper size (3/8") and it was clear inside.  I manifolded my 2 - 20# tanks into one to make sure I was sending an adequate amount of boiled off  LP gas volume to the furnace in the cold temps.  I made a Manometer to check the inches of water column reading coming into the furnace's gas valve and also what was exiting the gas valve, just before it entered the burner area.  Everything continued to check out.  In the end, a conversation I had with Empire stated that the 3-5" secondary flame height that is realistically  visable through that window is almost impossible to see......you probably  are OK at what you are seeing.  I had no past experience with these types of heaters and I guess I always thought it would throw more heat, so that kind of kept me chasing deeper and deeper to find a problem, but I don't think a problem really ever existed.  They take a little time to heat up and start "radiating"" some heat, or you can put in the fan kit and start getting more heat out of it a little quicker.

Share this post


Link to post
Share on other sites

I bought 2 fans off Amazon for $18 each and there 110v. There 5"x 5" and about 4" deep. I was thinking about mounting them under the heater. Or would it be better to but them in a woodbox and mount on to?. They say there good for 69,000 hr of run time.

Share this post


Link to post
Share on other sites

The fans I was talking about are 12 volt and only 1" deep. Putting them under the heater might not do the job because the heat from heater rises. If you have room in the lower cabinet on your heater you could mount one fan inside and blow the heat out the grill on the front of the heater.

Share this post


Link to post
Share on other sites

I think everybody goes through it after they first light their empire up.

mine was heating up slow thought it was the heater maybe the bend in the gas line

was pinching the gas off.  nope that was not it still could not get that secondary burner going.

My biggest problem was my fish house heated up slow. 

I looked at it this way a big buddy is 18000 btu this is only 15000

I is what it is. It is a good heater once every thing is up to temp.

Share this post


Link to post
Share on other sites

They are great heaters! Put your fans under them blowing into the cabinet, the object is to bow the heat off the exchanger 

Edited by Hawg

Share this post


Link to post
Share on other sites

I put a fan at the bottom to try to pull heat out the bottom that is not working very well.

I like your idea.

I think I'm going to rewire it so it runs back words at least blows heat it out of the top. 

They show a 110v fan for these heaters do they move air out the top or the bottom?

Share this post


Link to post
Share on other sites

I have one of these fans that came with my one I bought, I am taking it out as i don't want power, my shack is really only a day shack and stays at my cottage.  My fan is mounted on a the bottom of my empire 15k.

Share this post


Link to post
Share on other sites

I just checked on the fans that I bought, there 4.7 inchs sq and 1.25 thick. I thought they were 5 inch thick but I was wrong. They are 110v and I think I will put one inside on the bottom plate and see how it works. And I like where you have your fishingstar.

Share this post


Link to post
Share on other sites

Hey Star, I wouldn't leave the fan there. It's going to get really HOT and will melt ! Move it to the bottom of the cabinet just left of the gas valve and have it blowing up so it pushes the heat out the vents on the top half of the heater.

Share this post


Link to post
Share on other sites

I had the heater running for about 2 hours at 70 degrees.

The fan was hot but not to the point of affecting the fan.

This winter might be different when it has to run longer.

I was hopping to blow the air out the bottom of the heater.

I will do another test run later this week when it is colder out

I did have it lower I will just have to move it back.

Share this post


Link to post
Share on other sites

Fish, The idea is to force air from the bottom of the cabinet up past the heat exchanger and out the vents at the front top of the grill. If you put the fan at the bottom of the cabinet and space it up off the metal a inch or so it will draw air from the inside of the fish house and push it up past the heat exchanger where it will get warm and be forced out into the house. The fan should NEVER get HOT !

Share this post


Link to post
Share on other sites

I agree with Hawg and Sea Hage. This is a convection heater and heat rises through the top vents. At 15k BTU the area where you put the fan will reach 300+ deg. f. and deform the fan blades as they are made of plastic. Put the fan at the bottom as suggested. Your main objective is to get hot air circulation through the house. The floor will usually be cooler due to the holes but with the fan blowing at the bottom cold air is returned at the bottom of the heater through circulation. My house is same size as yours. I have a 9k BTU Dura Flame convection heater and tried several fan configurations. I did burn up the fan blades when installed as in you pic running at about 7k BTU. I than converted it to a forced air with air flow fan control using temperature controlled relays. The burner I posted earlier is from that heater where I increased the BTU to 12k. The temp in my house is very consistent floor to ceiling and operates same as my home furnace. May be a bit of overkill for what your looking for but really works well with great comfort at any outside temp and wind.

 

The bump  on the air duct has 3 four inch compute fans to maintain. Behind the white framed box I put a 4 speed auto fan for fast warm-up I turn off when warm. Runs at 12.5k BTU. The pipe duct going to the door I added this fall to heat my attached flip. Cold air return is opening below the heat chamber and at the auto fan.

Housein1 (700x394).jpg

 

When I am not in the house and want to keep it warm, I turn off the temp control relays and open the door to the original convection and turn the heat down.

Htr 1 (700x394).jpg

 

Share this post


Link to post
Share on other sites

Regardless of where you put that fan you'll still need another fan of some sort to circulate the air around the house. The heater one only get the air out and off the heat exchange. Put one or two more in the upper corners blowing the air back down. Hugger style ceiling fans if you have room are the best. The blades need at bare minimum 4 inches and most experts say 8 inches of clearance to the ceiling. I'm at about 4 1/2 and it works fine. 

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now




  • Posts

    • That would be a cool ride for the kiddo! Well done
    • Musky999 captured win number 3 on the season with a score of 337 2--BlackLundProV  319 3--fishingstar           312 4--Swiveldigger        298 5--88fan                    295 6--Catzman              280 7--mnwildman         268 8--gregg52               264 9--Juneau4              260 10-jar jar                  253 11-Henry's Heroes  251 11-huckfin               251 ---------------------------------------------------------------------------------------------------- Season Pts 1--Juneau4             8406 2--Swiveldigger      8344 3--Catzman             8341 4--mnwildman        8313 5--huckfin                8309 6--Musky999           8171 7--fishingstar           8122 8--88fan                    8094 9--Henry's Heroes   8055 10-jar jar                    7882 11-gregg52               7813 12-BlackLundProV   7757
    • Stumbled on this thread and nice to see that cool truck! That's is a sweet find. Reminds me of the project truck of my buddy's uncle. 1992 F150 2x4 6" suspension lift, Motometal forged wheels, and 33" tires.
    • Sacrilege!! Burn him! Burn him! 
    • Picked up a beat up old snowmobile sleigh with holes and cracks for cheap. 20 years in fiberglass mfg helped a lot! Fun little project to haul the grandsons around for some ice fishing and trail riding.
      Still need to add the windshield. I call it the "Monster Hauler!"
    • Agree to the fact that sometimes things we smoke do add up money wise.  I smoked 35 pounds of goose sausage today for the kid, spent around 100 bucks, trim, seasonings, casing etc.  But......... i got to drink about 13,14 and watch the queens while i did it, thats why I smoke. lol
    • From the tree I assume, not the stand.  But close for sure!  Nice to have a 10 pointer down (and all the other stuff) by this time of year.
    • Sucks to be you, I guess. You really don't know much about BBQ, do you?  
    • Except your thesis is contradicted by the fact that much BBQ doesn't really have much in the way of "strong spices".   
  • Our Sponsors